Smart UPS 1500 - Replaced Battery, now it won't stop beeping.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1500 - Replaced Battery, now it won't stop beeping.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
11
14103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:42 AM

Smart UPS 1500 - Replaced Battery, now it won't stop beeping.

I have several Smart UPS 1500's, and I have changed batteries many times. Yesterday, however, when I put a new battery in one of my units I had a problem. The UPS just keeps beeping, and saying "replace battery" with the new battery pack installed. Is there a way to clear this, or is the battery pack bad? It is a genuine APC battery pack... so I find it hard to believe it would be bad out of the box...

Thanks!
-Jim

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

Did you run a self-test on the unit after replacing the battery? It doesn't know when you actually replace the battery with a new one, so it's probably still reporting the "replace battery" alarm from before that never cleared. Running a self-test should clear that.

Message was edited by: buzz

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

per the instructions, you have to let the unit charge before you do that. The new battery is not charging.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:42 AM

I have several Smart UPS 1500's, and I have changed batteries many times. Yesterday, however, when I put a new battery in one of my units I had a problem. The UPS just keeps beeping, and saying "replace battery" with the new battery pack installed. Is there a way to clear this, or is the battery pack bad? It is a genuine APC battery pack... so I find it hard to believe it would be bad out of the box...

Thanks!
-Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:42 AM

Jim,

I would like to gather some more information from you to find the root cause of the issue. What lights are on the front of the UPS? Is the Replace Battery Light flashing or Solid? What is the version of Power Chute which you are using to monitor the UPS? What type of cable is connected between the UPS and Computer? Is it Serial or USB? If possible, could you please swap the batteries from other Identical working unit and check if the UPS in question works fine?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

Did you run a self-test on the unit after replacing the battery? It doesn't know when you actually replace the battery with a new one, so it's probably still reporting the "replace battery" alarm from before that never cleared. Running a self-test should clear that.

Message was edited by: buzz

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

My quick guess would be that you replaced the battery in the 1500 by hotswapping it, and the beeping wouldn't stop even after the self test. What worked for me before was to turn off the unit, unplug the unit from utility power, unplug the battery. Let it sit for a few second and plug it all back in. When the unit runs the self test when it turns on, it can flush the error.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

ON-LINE is 'ON', Replace Battery is 'FLASHING'. Unit is beeping. I put the old battery back in, and it returned to a normal state. I sent the battery back as an RMA, and the replacement unit does the same thing. This unit is not connected to anything via USB/SERIAL, and I am not running PowerChute s/w.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

I installed PowerChute, and it's very puzzling. With the new battery installed, PC indicates that the old battery is still in there. It also thinks the UPS is working perfectly, even though the replace battery light is blinking on the unit. I tried a SELF-TEST, and it just sits there thinking that it's running, but it isn't. I also tried a calibration, that didn't work either. If I put the original battery back in the unit, it seems to function just fine. I cannot figure this one out. It will not take a new battery.

-Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

Jim,

The Flashing Replace Battery Light+ indicates that the batteries are not connected or recognized by the UPS. I suspect that the new battery is most likely the root cause of the issue.However, I need some more information from you to confirm you the root cause. Could you please let us know the exact Model and Serial number of the UPS? You can find these details on a white bar code sticker at the rear of the unit. Could you please let us know the new RBC part number? Could you please double check if the New battery is connected to the UPS firmly?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

I messed with this for about TWO HOURS. Although I still do not understand what the issue was, I do have the UPS working again. I put a battery from another 1500 into the unit I was having trouble with, and it recognized the battery and is working fine. I put the new battery into the 1500 that I stole the battery from for the first step, and it worked fine as well. No matter what I tried, the new battery would not work in the first 1500.

S/N for the first 1500 is "AS0308331463", Mfr Date 02/20/2003, Firmware Version 601.3.D - this was the UPS I was having trouble with
S/N for the second 1500 is "AS0442332141", Mfr Date 10/15/2004, Firmware Version 601.3.D - this is the UPS I took a battery from

Both Batteries are RBC7 (Genuine APC)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

per the instructions, you have to let the unit charge before you do that. The new battery is not charging.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:09 PM . Last Modified: ‎2024-03-14 03:42 AM

I am giving this a try now. It sounds feasable. I guess the term "Hot Swappable" has a different meaning over at APC....

Reply

Link copied. Please paste this link to share this article on your social media post.

TrickyDick
TrickyDick
Cadet

Posted: ‎2024-11-30 11:38 AM

0 Likes
0
4462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-30 11:38 AM

I had the same beeping after replacing the battery.  I can gleefully report how silly that was.  I had UNPLUGGED the UPS before replacing the battery.  I FORGOT to plug the UPS back into the wall.  So of course it beeped, waiting for my grey matter to kick in, LOL.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.