APC Back-UPS BE850G2-GR battery problem or not?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Back-UPS BE850G2-GR battery problem or not?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Robert_Dev
Robert_Dev
Cadet

Posted: ‎2024-08-30 12:09 PM

0 Likes
2
1488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 12:09 PM

APC Back-UPS BE850G2-GR battery problem or not?

I bought the BE850G2-GR in november 2021. It always worked perfectly. Because of some changes in my meter cupboard, I have disconnected the UPS for about a month. Last week, I wanted to reconnect it, but when I power it on, the Power on/off LED flashes red and Battery status LED flashes green in quick
succession. Also, there is a constant tone.

 

In the manual, I have read that this means the battery is disconnected. However, the battery is connected properly. I tried ordering a new battery. It arrived todat, I connected it, but unfortunately the same thing happens: power on/off LED flashes red and battery status LED flashes green in quick
succession. The constant tone is there as well.

Anybody has an idea what could be wrong? It would be a shame if the UPC is broken after only 2,5 years. Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Teken
Kirk Teken
Kirk

Posted: ‎2024-09-02 06:29 AM

0 Likes
1
1472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-02 06:29 AM

Assuming the new battery is 100% SOC. You may consider doing a Brain Dead reset as outlined in these two links.

 

Follow the steps that relate to your specific model:

 

https://www.apc.com/us/en/faqs/FA156611/

 

https://www.apc.com/us/en/faqs/FA158947/

Let me know what you see and observe once the brain dead rest has been completed.

 

NOTE: It’s important to remember that the battery installation date be updated in the APC Power Chute Software prior to doing this step! ☝️

Reply

Link copied. Please paste this link to share this article on your social media post.

ZaneMagnum
ZaneMagnum
Cadet

Posted: ‎2024-12-01 10:08 AM

In response to Teken
0 Likes
0
1273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-01 10:08 AM

I have almost the same issue:

APC UPS BE850G2 purchased 06-24-2020. On a replaced battery 08-01-2024. Voltage tested @ 13.26v.

UPS has been on since replacement. The other day all my devices connected to the UPS showed it was disconnected, devices were on again. My NAS was not happy. So this happened 3 times in a short time span less than an hour, perhaps.

Second shut down (that I know of) and restart I noticed:

flashing green light, flashing red light, flashing amber light, shutdown in 5 seconds or so then the device turned back on. Crazy, like nothing happened. Then the UPS started beeping intermittently.

I unplugged devices, turned off the UPS, unplugged the UPS, the UPS restarted all by itself beeping since it was not plugged in, plugged UPS back in, device beeps a couple more times and stopped. UPS shows it's on. Plugged devices back in, 1 minute later UPS is on the fritz again.

Turned off, unplugged devices, Tested battery, still at about 13v...

Tested both brain dead reset and UPS didn't care it kept trying to turn back on when the battery was hooked back up. Every time I tried to turn of it will turn itself back on (of course with battery attached).

I decided to use the UPS in another room, this time the UPS shut down completely (different devices attached) less than 10minutes or so.

Unlugged all devices. Hit the ON button and it turns on. (It's not an overload of watts since I have not had an issue before in the original connection of devices.)
It's been about an hour with no devices connected and it is still on, no beeps or issues.

I am guessing the internal brain is retarded and should get a new UPS. and it's not the battery or is it.
Oh did I say I have another BE850G2 and there is nothing wrong with that one. (so far) 🙂
Any one have thoughts on this? Other than a ghost?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore