Smart-UPS 1500 Mysterious Battery Charge Drop from 100% to 5%

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 Mysterious Battery Charge Drop from 100% to 5%
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
trulifeoptics_apc
Crewman trulifeoptics_apc
Crewman

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:16 PM

0 Likes
2
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:16 PM

Smart-UPS 1500 Mysterious Battery Charge Drop from 100% to 5%

I was very surprised to receive a "Battery Discharged" notification earlier today from one of our older Smart-UPS 1500 units.

It has been working perfectly and had a couple of changes of batter. The last in March 2020.

Everything was fine until that unexpected notification. When I checked in PowerChute it said the batter charge was 5%! Yet how can this be when I received no other notifications. I know notifications about going on off batter are working fine, as are notifications such as "AVR Trim Actrive/No Longer Active". So why this sudden "battery discharged" without any warning?

First thoughts would be sudden overload. Yet the data log makes this even more mysterious.

This is the event log:

wIACCzRJiMvpvNFUK5sxYQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngwIACCzRJiMvpvNFUK5sxYQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngAnd this is the data log which is really puzzling:

9fAJzKcpESpKqtlymJqjtQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png9fAJzKcpESpKqtlymJqjtQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Absolutely NOTHING going on before the batter suddenly drops from 100% to (as shown) 7% !!?!?!?

Anyone any ideas or thoughts as to what the hell is going on?

George

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
trulifeoptics_apc
Crewman trulifeoptics_apc
Crewman

Posted: ‎2021-06-30 07:18 AM . Last Modified: ‎2024-03-07 11:16 PM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:18 AM . Last Modified: ‎2024-03-07 11:16 PM

It is really strange.

I've looked back through the data logs and the load occasionally going up to 19.5% is not that unusual. Never has it done that. Here is one from earlier in the same day, so I'm assuming it's just naturally variation in load due to stuff like hard drive access - it powers a server with a RAID 5 array of 15K drives and a QNAP 4 drive NAS box.

9asWOrVtd7agS1MpKcvHfw%3D%3D.png9asWOrVtd7agS1MpKcvHfw%3D%3D.png

I'm just wondering if it is some strange transient battery fault.

I've a much newer APC SmarUPS which I'll swap over next time I'm on site - just in case. I might try and run a battery calibration test tomorrow. However, due to COVID we have staff on site at all sorts of odd times currently to maintain social distancing and keep projects going in our labs. So little opportunity for scheduled down time.

Thanks for your comments.

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:16 PM

0 Likes
0
2413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:16 PM

Unusual as you'd expect a drop in battery voltage to accompany a drop in charge.  I notice your load increased from 17% to 19.5% at the time, so possibly something switched on which briefly drew a lot of power when it was switched on, causing the UPS to recalculate its battery capacity?

I had an issue with an older SmartUPS 1400 XL where it wouldn't run off the battery if the load was over around 60%, and when I tried to do a self test or calibration it would briefly click the inverter on and off and then the battery would suddenly say 0% and then start "charging".  When I removed some of the load and got it to start the inverter, it would go for 15 minutes on batteries that, when moved to a newer UPS, ran for an hour.  So I'm not sure of the age of your UPS but if it's of similar vintage to my 1400XL then I'm not sure I'd really trust it!

Reply

Link copied. Please paste this link to share this article on your social media post.

trulifeoptics_apc
Crewman trulifeoptics_apc
Crewman

Posted: ‎2021-06-30 07:18 AM . Last Modified: ‎2024-03-07 11:16 PM

0 Likes
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:18 AM . Last Modified: ‎2024-03-07 11:16 PM

It is really strange.

I've looked back through the data logs and the load occasionally going up to 19.5% is not that unusual. Never has it done that. Here is one from earlier in the same day, so I'm assuming it's just naturally variation in load due to stuff like hard drive access - it powers a server with a RAID 5 array of 15K drives and a QNAP 4 drive NAS box.

9asWOrVtd7agS1MpKcvHfw%3D%3D.png9asWOrVtd7agS1MpKcvHfw%3D%3D.png

I'm just wondering if it is some strange transient battery fault.

I've a much newer APC SmarUPS which I'll swap over next time I'm on site - just in case. I might try and run a battery calibration test tomorrow. However, due to COVID we have staff on site at all sorts of odd times currently to maintain social distancing and keep projects going in our labs. So little opportunity for scheduled down time.

Thanks for your comments.

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore