Smart UPS 1500 Battery Light

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1500 Battery Light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:36 AM

0 Likes
9
16486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:36 AM

Smart UPS 1500 Battery Light

Hello,

Our Smart UPS 1500 Model# SUA1500RM2U is apparently failing its self test. It is emitting short beeps for one minute and the replace battery indicator is constantly flashing. The strange thing is when we first noticed this about a month ago we unplugged the Smart UPS and it still continued to run every device we had plugged into it, all off of the battery. This was about a month ago and when we plugged the Smart UPS back in the Battery light turned off and everything seemed normal. Well a few days ago the Battery indicator came back on. This is what makes me unclear. Although it seems fairly obvious that the battery is on its way out, is there anything else I can do to confirm that this is in fact the issue before going out and replacing the battery? I am thinking there may be other reasons the self test could fail besides the battery. Hoping someone has some insight to share with me.

Thank you

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Thanks a lot. it worked. light is now off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Hello John,

A flashing replace battery light means that the UPS detects that there is no battery connected on it. Would you happen to have another UPS that is using the same kind of battery? If you do we can swap the batteries and check if the UPS would be able to recognize the new battery that is attached on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

when the LED is flashing, it means the UPS thinks the battery is disconnected, versus needing to be replaced. this can happen when its disconnected or when the voltage is really low on the battery and it cannot detect that it is actually connected.

how old is the unit? the first few digits of the serial number will tell us, if you arent sure - like AS0735

some things i would try:

1.) if you have a network management card/powerchute software, check the logs inside of there and also check the battery voltage reading via that method
2.) if you dont have any software/NMC, check the battery voltage with a voltmeter.
3.) have you tried the pull plug test recently? if you do, you may want to with some non-critical equipment incase it does fail.

this should be a good start. hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Gentelmen,

Thank you very much for your responses. From my understanding of that particular Replace Battery LED it can indicate one of two things: 1.) the battery needs replaced and the device will emit beeps for one minute and the LED is illuminated. 2.) the battery is disconnected and a short beep is emitted every two seconds to indicate the battery is disconnected.

The behavior our Smart UPS 1500 is exhibiting is more like the 1st scenario. It beeps for a about a minute every half hour or so and the Replace Battery LED is constantly illuminated. As to both of your replies;

I picked a winna: I am not sure how old the device is but the serial number is A50548134296. To my knowledge there is no network management / powerchute. If there is a definitive way to check that the device supports it but the management has not been setup I would love to know. I have not tested the battery with a voltmeter but I could give that a shot. I have pulled the plug once again about a month ago. The battery held a charge and the equipment it was powering ran fine.

JonPo: I do not have access to another similar device at the moment. I am in the process of pricing out a new battery for this unit.

I am just looking for confirmation that the battery is in fact the issue. I will try and test the battery with a voltmeter and maybe try unplugging the device again. If you have any other suggestions I would love to hear them in the meantime I will post back in a day or two with any further results.

Thanks again guys

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Thank you very much for your responses. From my understanding of that particular Replace Battery LED it can indicate one of two things: 1.) the battery needs replaced and the device will emit beeps for one minute and the LED is illuminated. 2.) the battery is disconnected and a short beep is emitted every two seconds to indicate the battery is disconnected.
The behavior our Smart UPS 1500 is exhibiting is more like the 1st scenario. It beeps for a about a minute every half hour or so and the Replace Battery LED is constantly illuminated. As to both of your replies;
I picked a winna: I am not sure how old the device is but the serial number is A50548134296. To my knowledge there is no network management / powerchute. If there is a definitive way to check that the device supports it but the management has not been setup I would love to know. I have not tested the battery with a voltmeter but I could give that a shot. I have pulled the plug once again about a month ago. The battery held a charge and the equipment it was powering ran fine.
that serial number indicates the UPS is close to 5 years old and then assuming they are original batteries, they are close to 5 years old too. batteries typically last 3-5 years so it makes sense that you appear to be due for a battery replacement. this UPS supports either powerchute business edition (free software) with use of the APC serial cable (part number 940-0024 or 940-1524 - any other serial cable would most likely drop the load on the UPS so ensure you have the correct cable) or the USB cable that would have come with the unit. on this unit, i believe it has a USB A connection so you use a USB A to B. with the powerchute software, you could check out the status of the unit, including battery voltage. a network management card is an added accessory that connects to the UPS smart slot. a part number for that would be [AP9630 or AP9631|http://www.apc.com/products/family/index.cfm?id=98] if you're interested.

you could start with powerchute business edition, available on apc.com, if you find the correct cables, rather than using a voltmeter. jonpro's suggestion will ultimately also help us decide what the issue here but if these are original batteries, i would have to make a highly educated guess that the batteries are on their way out and you may just need new ones.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Winna:

Thanks for the insight it is greatly appreciated. I actually went ahead and ordered a new battery kit from Newegg. I should get around to installing them this weekend or shortly thereafter. I will also look into the powerchute software as well at least if not for future reference. I will report back when I have successfully swapped the batteries out.

Thanks again

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

welcome. talk to you soon.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Hi there,

we have this SMX1500RM2UNC with the red battery light blinking still after we changed the battery with a new one. have not rebooted the SmartUPS as yet.. will this fix the blinking issue? by the way.. the unit is not beeping. just blinking... battery shows 100% charge.

thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Hi,

You should run a self-test to clear the replace battery indicator. There is no need to reboot the UPS. For assistance with initiating a self-test see Schneider Electric FAQ FA156584 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
16479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Thanks a lot. it worked. light is now off.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.