Server Shuts down even though option is disabled

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Server Shuts down even though option is disabled
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
117
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
4
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Server Shuts down even though option is disabled

Hello, i have powerchute installed on a server but I have all the shutdown options disabled as the server is running dual PS attached to 2 UPS's (i just want to use the powerchute software to monitor the UPS, not to initiate any shutdowns).

Problem is over the weekend I got  emails "Battery Disconnected" followed by "Insufficient Runtime Available".  So I know i need to look at replacing the UPS or the battery, but the problem is immediately after this, Powerchute shut my server down.  

I confirmed, in the Powerchute - Event Configuration "Shutdown" is unchecked on every option.  In addition in the "Shutdown Settings" configuration, it is set to "Do not shutdown when power fails".

What am I missing?  I do not want the server to shut down on power failure.

Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Chris,

PCBE is designed to power down the system for Low Runtime Remaining See the chart below

Even though you deselected any event shutdowns and select Do not shut down when power fails if the battery runtime falls below the combined time configured for Application and Operating System shutdown the system will be commanded down. 

This screenshot is from the PCBE help file

It states that Low Runtime Warning event does not display on the Event Configuration screen as it is not configurable (because it always causes a shutdown). The application is designed that way to prevent the OS from crashing. 

If you are uncomfortable with this you can uninstall PCBE and install a NMC in the UPS to monitor the UPS that way. Another possible option is to install APCUPSD. To my knowledge APCUPSD can be configured to never shut down the OS but I recommend checking with the APCUPSD forum to verify. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Chris,

What version of PowerChute are you running? PowerChute Network Shutdown or PowerChute Business Edition and if PowerChute Business Edition is the server and console installed? 

Depending on the version of PowerChute when 2 critical events occur simultaneously a shutdown will be triggered.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

It is power chute business edition.  I do have the server and the console installed.

If there is no way to totally disable an auto shut down i may just need to remove the software, but i like being able to monitor the status of the UPS's so ideally i could keep it and just disable the auto shut down.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

FYI Here is the event log for the time it shut down:

Event Log

12/5/15 09:59:48 Monitoring Stopped
12/5/15 09:59:48 PowerChute Agent outlet turning Off
12/5/15 09:59:48 Insufficient Runtime Available
12/5/15 09:59:46 Online (Green Mode) - Exited

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

0 Likes
0
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:26 AM . Last Modified: ‎2024-03-13 05:35 AM

Chris,

PCBE is designed to power down the system for Low Runtime Remaining See the chart below

Even though you deselected any event shutdowns and select Do not shut down when power fails if the battery runtime falls below the combined time configured for Application and Operating System shutdown the system will be commanded down. 

This screenshot is from the PCBE help file

It states that Low Runtime Warning event does not display on the Event Configuration screen as it is not configurable (because it always causes a shutdown). The application is designed that way to prevent the OS from crashing. 

If you are uncomfortable with this you can uninstall PCBE and install a NMC in the UPS to monitor the UPS that way. Another possible option is to install APCUPSD. To my knowledge APCUPSD can be configured to never shut down the OS but I recommend checking with the APCUPSD forum to verify. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of