Smart-UPS 1400 serial connection kills power to UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Slider_apc
Crewman
Crewman
0 Likes
3
214

Smart-UPS 1400 serial connection kills power to UPS

This was originally posted on APC forums on 2/17/2008


I just purchased two used Smart-UPS 1400s, which utilize a serial connection. When I connect the serial cable to my server, then plug it into the UPS, it immediately kills the power to the UPS and thus, my server.

I assumed they use a standard db9 RS232 connection. Is that not right?

I tried this with and without having PowerChute installed. It made no difference.

When the serial cable was attached at both ends, I could not even turn the UPS on. I had to disconnect the cable from the UPS in order to power everything back up.

Any advice and insight would be much appreciated.

tia.


Accepted Solutions
KVAr_apc
Captain
Captain
0 Likes
0
214

Re: Smart-UPS 1400 serial connection kills power to UPS

This was originally posted on APC forums on 2/19/2008


Slider wrote:
Thanks for the reply.

As I purchased them used, they didn't come with cables. I'll see if I can find some.


Todd.
You can get a 940-0024C or it's generic equivalent. It's not that difficult to make one out of a regular serial cable either if you want.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
214

Re: Smart-UPS 1400 serial connection kills power to UPS

This reply was originally posted by Annie on APC forums on 2/17/2008


Hey,
You need to use the cable shipped with the UPS. Its part number should be 940-0024C or 940-0024D, or 940-1524C or 940-1524D , this depends on what specific UPS model you are using.

Slider_apc
Crewman
Crewman
0 Likes
0
214

Re: Smart-UPS 1400 serial connection kills power to UPS

This was originally posted on APC forums on 2/18/2008


Thanks for the reply.

As I purchased them used, they didn't come with cables. I'll see if I can find some.


Todd.

KVAr_apc
Captain
Captain
0 Likes
0
215

Re: Smart-UPS 1400 serial connection kills power to UPS

This was originally posted on APC forums on 2/19/2008


Slider wrote:
Thanks for the reply.

As I purchased them used, they didn't come with cables. I'll see if I can find some.


Todd.
You can get a 940-0024C or it's generic equivalent. It's not that difficult to make one out of a regular serial cable either if you want.