Anyway to use rack power distribution unit application apis from an angular front end?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Anyway to use rack power distribution unit application apis from an angular front end?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
agalu129_apc
Ensign agalu129_apc
Ensign

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:30 AM

0 Likes
8
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:30 AM

Anyway to use rack power distribution unit application apis from an angular front end?

Hi there,

I'm working on an application that will be able to control power switches located on the rack power distribution unit application. Is there anyway to whitelist my angular front end application so that i can make post and get requests to the rack power distribution unit application apis? I tried calling the apis but keep getting an "No Access-Control_Allow-Headers" error. I looked further into this and it seems my frontend requires a nmc object key that is used in the endpoint. (e.g http://xxx.xx.xxx.xx/NMC/kQtlr8AEz8bRMchJ73RGiA/home.htm . But I'm not sure on how to retrieve this key as I assume this key is retrieved when logging into the application. I also tried calling the login apis first but still get Access-Control-Allow-Headers errors. Any help would be great.

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • api
  • application
  • distribution
  • power
  • rack
  • unit
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

That's not really how SNMP works.

The commands are standard for all SNMP devices the only thing that changes is the target OID and the value set. The list of OIDs associated with the PDUs can be found in the Powernet MIB. (Like I said you'd need to be familiar with SNMP)

-Gavan

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:30 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:30 AM

I don't think this method is supported but for what your trying to accomplish I'd recommend using either an SSH script that will log-in and run the command to control the outlets or using SNMP to turn the outlets on or off.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

agalu129_apc
Ensign agalu129_apc
Ensign

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

I've opted to use a nodejs server to that communicates with the pdu whenever my web app makes a request. The nodejs server will send ssh commands to the pdu. I was wondering though if there is any documentation on what ssh commands I can use to communicate with the pdu to login, turn on/off switches?

 

Thanks for the help,

Albert

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

The easiest way is to log into the PDU via SSH and then issue the ? command, some commands are slightly different for different units and firmwares:

apc>?

System Commands:
---------------------------------------------------------------------------
For command help: command ?

? about alarmcount boot bye cd
clrrst console date delete dir dns
eapol email eventlog exit firewall format
ftp help lang lastrst ledblink logzip
netstat ntp ping portspeed prompt pwd
quit radius reboot resetToDef session smtp
snmp snmptrap snmpv3 system tcpip tcpip6
user userdflt web whoami xferINI xferStatus

Device Commands:
---------------------------------------------------------------------------
alarmList bkLowLoad bkNearOver bkOverLoad bkReading bkPeakCurr
bkRestrictn devLowLoad devNearOver devOverLoad devReading devPeakLoad
devStartDly dispID humAlGen humLow humMin humHyst
humReading humStatus lcd lcdBlink logToFlash olAssignUsr
olCancelCmd olDlyOff olDlyOn olDlyReboot olGroups olName
olOff olOffDelay olOn olOnDelay olRbootTime olReboot
olStatus olUnasgnUsr phLowLoad phNearOver phOverLoad phReading
phPeakCurr phRestrictn prodInfo sensorName tempAlGen tempHigh
tempMax tempHyst tempPeak tempReading tempStatus userAdd
userDelete userList userPasswd

apc>olOff ?
Usage: olOff -- Turn an outlet or group of outlets off.
The id# may be from 1 up to 32 depending on NPS group size.
olOff [:]

 

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

agalu129_apc
Ensign agalu129_apc
Ensign

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

Thanks for the response Gavan. Do you know if the rack pdus generate a privateKey that I can use to ssh and authenticate myself into the pdu?

Reply

Link copied. Please paste this link to share this article on your social media post.

agalu129_apc
Ensign agalu129_apc
Ensign

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

Also where can i find this private key once sshed into the rack pdu?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

The SSH implementation doesn't support key authentication, you'll need to provide a user name and password.

If you want an easier to implement option the I still recommend SNMP, this command will turn of outlet 1 immediately: 

(Easier in terms of implementation, you'd need to understand how SNMP works first undecided) 

snmpset -v 1 -c public 192.168.0.1 1.3.6.1.4.1.318.1.1.12.3.3.1.1.1 i 2

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

agalu129_apc
Ensign agalu129_apc
Ensign

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

Thanks I will probably use SNMP instead then. Where can I see the commands I can use for SNMP? Can't seem to find any instruction in the documentation for the Rack PDUs. Also would I be able to authenticate into the PDUs with just a username and password because that is all I have access to at the moment?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:09 AM . Last Modified: ‎2024-03-08 01:29 AM

That's not really how SNMP works.

The commands are standard for all SNMP devices the only thing that changes is the target OID and the value set. The list of OIDs associated with the PDUs can be found in the Powernet MIB. (Like I said you'd need to be familiar with SNMP)

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore