Smart-UPS 1400 RM XL Radius authentication

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1400 RM XL Radius authentication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
5
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

Smart-UPS 1400 RM XL Radius authentication

Does anyone know how the Radius authentication works on this device? When I turn on Radius, I chose the option for "RADIUS, then local".

Then when logging in with RADIUS credentials it only let's you in as a read only user and you can also no longer logon with the local admin account.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:27 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:27 PM . Last Modified: β€Ž2024-03-15 12:30 AM

Thanx Winna! Knowing that it is failed connectivity and not failed "authentication" as the doc states makes all the difference. Stopped the IAS service for a minute and wha-la.

Forever Greatful,
Todd

Message was edited by: Fremont

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

See [this document|http://www.apcmedia.com/salestools/ASTE-6Z5QC8_R0_EN.pdf] detailing how to set up the RADIUS server. Unless you specify the service-type of a user, it defaults to read-only.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

But that does not explain why the local account no longer works:

RADIUS then Local: RADIUS is enabled, and local authentication is
enabled. Authentication is requested from the RADIUS server first;
local authentication is used only if RADIUS authentication fails.

This does not seem to be the case as the user and password I used to config radius is a local account and once I configured Radius the local credentials no longer work.

How can I get back to a point of being able to configure this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:26 PM . Last Modified: β€Ž2024-03-15 12:30 AM

the local account will only work if RADIUS fails. RADIUS failing is when the RADIUS server is unreachable. it is not considered a failure if the RADIUS server is reached and the username/password is incorrect.

if you have the same username set up for the RADIUS account as the local account, i think you will run into problems. if the username is not set up on the RADIUS account, it will not authenticate and not let you login because the RADIUS server responded.

the easiest way to fix this that i see is:

configure an acceptable username/password on the RADIUS server so the NMC can hit the RADIUS server and authenticate

or

disable the RADIUS server so that it is in accessible over the network, and it will fail because its unreachable, and then it will allow local access. this might not be a good idea because i imagine your RADIUS server is in production..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:27 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:27 PM . Last Modified: β€Ž2024-03-15 12:30 AM

aww glad i could help πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:27 PM . Last Modified: β€Ž2024-03-15 12:30 AM

0 Likes
0
1478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:27 PM . Last Modified: β€Ž2024-03-15 12:30 AM

Thanx Winna! Knowing that it is failed connectivity and not failed "authentication" as the doc states makes all the difference. Stopped the IAS service for a minute and wha-la.

Forever Greatful,
Todd

Message was edited by: Fremont

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore