Smart UPS 1400 Fan Constantly On

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 1400 Fan Constantly On
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
5
2354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

Smart UPS 1400 Fan Constantly On

I have Smart UPS 1400 that is probably close to 10 years old (yeah - I should replace the batteries). But this week something weird started to happen. The fan now runs constantly. I have completely shutdown the unit and performed the self test. But the fan keep running nonstop? Does anyone know a way to fix this problem?

Many thanks,
Alex

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • cooling
  • hardware
  • smart-ups
  • smartups_1400
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

Thanks for the service center recommendation.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
0
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

The SU1400NET turns on the fan when power going to the battery exceeds a certain threshold, which I've yet to measure. Parasitic charging current increases with battery age. Perhaps your battery pack have deteriorated to this point?

Power up completely and disconnect the battery while power is on. This should kill the fan within a few seconds if there is no internal problem. If it doesn't, there's an internal fault.

Have you performed a load test? The unit should run at least a few minutes with 500W load. (new battery gives 20+ min).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

Hello,

Here are our Fan Operation Parameters for SmartUPS:

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=6672

If the fan is still spinning beyond these parameters, more than likely there is a fan control sensory fault in the UPS. A constant fan is not something to be overly concerned with in actual UPS production. As long as the UPS is still providing proper power whether online or on battery, having your fan spin constantly shouldn't be a great concern.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

If the fan is still spinning beyond these parameters, more than likely there is a fan control sensory fault in the UPS.
A constant fan is not something to be overly concerned with in actual UPS production. As long as the UPS is still
providing proper power whether online or on battery, having your fan spin constantly shouldn't be a great concern.
My SU1400NET has an always-on fan also, even when no equipment is connected to it (i.e. no load) and the battery charge indicator LEDs show full charge so I assume that charging is minimal.

I am using this unit in a home office and while it appears to be working fine other than the fan spinning constantly, the noise of the fan is the loudest thing in the office. Is repairing a "fan control sensory fault" a component-level repair or will an entire board need to be replaced?

Or, I suppose more accurately, is this an easy fix (i.e. inexpensive) or a one that is not?

Is there an authorized service center in central Maryland (21755) or do I need to ship the unit directly to APCC?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

APC does not repair these units in house. I am not sure what type of repair would be in order for that. APC's authorized repair center is Coastal Business Machines. Their website is www.cbmi.com

and just to note, on our newer units, such as the SUA1500 which is the replacement for the SU1400, the fans now are designed to run all the time but they have two speeds. a low speed that the UPS runs at majority of the time and then a higher speed when the battery is charging, the load is above 75%, the internal temp goes above 104º or if the UPS is running on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

0 Likes
0
2354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 PM . Last Modified: ‎2024-03-15 04:00 AM

Thanks for the service center recommendation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore