Help!
I installed new batteries into the UPC (very low voltage output from the two-batteries, roughly 1.3V). After that, I get no response from the UPS. No lights on or flashing, no beeping... nothing.
If I re-install the old batteries (roughly 13v between them), then this constant chirping and green LED flashing continues indefinitely.
Here are two very short YT video that shows the beeping / flashing:
https://youtu.be/SCYzyDyWCJY
https://youtu.be/NA4PB4lwE1I
The beeping / flashing is slowing down over time, fyi...
Thank you!
John
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:10 PM . Last Modified: 2024-03-15 04:17 AM
With "new" batteries sitting at 1.3 volts you can consider those batteries dead, gone, kaput. Basically that's saying that five of the six cells in the battery are gone totally flat. The UPS would not even be able to consider the "new" batteries installed at that point. Replace the batteries with known good ones.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:10 PM . Last Modified: 2024-03-15 04:17 AM
With "new" batteries sitting at 1.3 volts you can consider those batteries dead, gone, kaput. Basically that's saying that five of the six cells in the battery are gone totally flat. The UPS would not even be able to consider the "new" batteries installed at that point. Replace the batteries with known good ones.