Hi all
Just want to know what is Low dc warning and low dc shutdown, this log was came from the UPS, Also i wonder in NMC AP9617 i didnt get this alarm instead i get the UPS: Batteries discharge, UPS: Batteries discharge condition cleared, UPS: Batteries weak.
Are this type of alarm is the same?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
did you perform power failure simulation?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:28 AM
Checking with the three phase team now to address your question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:28 AM
Low DC warning and Low DC shutdown are warnings that are specific to Silcon units that are on battery (or think they are on battery) and about to shut down. It is similar to a "low battery duration" alarm on other UPS systems. Batt disch. and batt weak messages you got refer to low batt voltage. It is recommended that you call into technical support to discuss possibilities for troubleshooting or battery replacement. Tech. support can be reached at 1-800-800-4272 and you will need to choose the three-phase/Symmetra PX/Megawatt option.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:28 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:28 AM
thank you very much for clarifying the issue,
One more thing, the boss told me that they are just changing the batteries last few weeks,
so is there any possibility that the batteries have some issue? thanks again
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:28 AM
It is possible that the batteries were weak or going bad...and if so then new batteries would likely fix the issue. If you are referring to some "new" batteries having issues...that's beyond my capacity to say since Silcon battery systems are not my specialty. However, your best source for a confirmation would be our three-phase tech support team.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
ok,
just for the record, can the silcon do the runtime calibration? just like other small ups, provided the silcon came with NMC and tripple chasis.,
BTW, if we perform runtime calibration its better to have load or not?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
dear sir,
i have the same problem "low dc warning and low dc shutdown", would you please tell me if you resolved it and how?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
dear sir,
i have the same problem "low dc warning and low dc shutdown", would you please tell me if you resolved it and how?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:29 AM . Last Modified: 2024-03-19 01:27 AM
did you perform power failure simulation?
Link copied. Please paste this link to share this article on your social media post.