APC AP9617 Not Logging events to Management Card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP9617 Not Logging events to Management Card
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
11
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

APC AP9617 Not Logging events to Management Card

I have 4 APC-AP9617's and only one of the units is logging temporary loss of power to the Management Card. We seem to have a brown out every morning and all 4 unites log the event on the units console; however, if you log into the remote management through http, you do not see this event on 3 of the units.

Any ideas on why this might happen. All 4 are running the same firmware, configured identical from a HTTP perspective.

The outage is normally only 2 - 5 seconds.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

this thread is a few years old. lets make sure you are up to date on your firmware - AOS 3.7.3 and sy3p 3.7.2 if this is a symmetra 3 phase unit as well. also, what are your IM revisions?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

are they all inside the same model of UPS? either way, what UPS model(s) are we talking about?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

Stephen,

Do these cards have the same configuration when it comes to notification/logging? You can try to download the config.ini of the working card and upload it on the 3 other cards

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:28 AM . Last Modified: ‎2024-03-19 01:28 AM

3 of the unitx are Symmetra 40K THORC456, These are not alerting on the 4 - 5 sec outages.

The other is a Symmetra 80K THORC456, alarms are working correctly.

I'm not sure how to download the config.ini, I'll look that up and see.

Thanks for the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

They do all have the same configs, we set them side by side and validated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

i believe that the intelligence module firmware can be found in the Diags Menu on the powerview under Intelligence modules or in the management card interface under Detailed Status->Intelligence System->Firmware Revision

i would download the config.ini of the cards via the instructions i had posted and we can compare this. this information you posted is good to know but doesn't necessarily matter in relation to this problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

how did you view the configs side by side? on what screen of the management card.

[here is how to download the config.ini|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8789]

i vaguely remember hearing something about depending on the intelligence module firmware on the symmetra PX, short outages (on battery events) arent recorded.

i am not a three phase symmetra expert though..if you contact APC three phase support though they may be able to shed light on the issue. if you cant let me know, i will try to have them take a look at the thread.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

I did a side by side comparision. I've validate that the Unit itself does record the problem; however, the management card does not.

This is the information on the working unit.

Hardware Factory

Model Number: AP9617
Serial Number:
Hardware Revision: A10
Manufacture Date: 01/23/2003
MAC Address:
Management Uptime: 20 Days 18 Hours 34 Minutes

Application Module

Name: sy3p
Version: v3.5.7
Date: 08/13/2008
Time: 22:13:41
APC OS (AOS)

Name: aos
Version: v3.6.1
Date: 08/13/2008
Time: 18:49:49

This is the information on the non working unit.
Hardware Factory

Model Number: AP9617
Serial Number:
Hardware Revision: A10
Manufacture Date: 07/15/2003
MAC Address:
Management Uptime: 20 Days 18 Hours 53 Minutes

Application Module
Name: sy3p
Version: v3.5.7
Date: 08/13/2008
Time: 22:13:41

APC OS (AOS)
Name: aos
Version: v3.6.1
Date: 08/13/2008
Time: 18:49:4

How can I confirm the version of the management modules?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

Below is the information you asked for. I'll pull the config.ini and look at them.

Main Intelligence Module (MIM)
Module Status:
Status Good On & OK
Serial Number: PD0550132383
Manufacture Date: 08/28/08
Firmware Revision: 20.00
Hardware Revision: B
Redundant Intelligence Module (RIM)
Module Status:
Status Good On & OK
Serial Number: PD0646132665
Manufacture Date: 08/26/08
Firmware Revision: 20.00
Hardware Revision: B
Internal Communication Status
Communication Status:
Status Good OK
MIM Internal CAN Bus: OK
MIM External CAN Bus: OK
MIM <--> RIM CAN Bus: OK
RIM Internal CAN Bus: OK
RIM External CAN Bus: OK


====================================================================
Main Intelligence Module (MIM)
Module Status:
Status Good On & OK
Serial Number: PD0502110865
Manufacture Date: 01/05/09
Firmware Revision: 20.00
Hardware Revision: B
Redundant Intelligence Module (RIM)
Module Status:
Status Good On & OK
Serial Number: PD0618130642
Manufacture Date: 01/05/09
Firmware Revision: 20.00
Hardware Revision: B
Internal Communication Status
Communication Status:
Status Good OK
MIM Internal CAN Bus: OK
MIM External CAN Bus: OK
MIM <--> RIM CAN Bus: OK
RIM Internal CAN Bus: OK
RIM External CAN Bus: OK

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

ok. all of that looks good. 20.00 is the latest revision for the power modules - which you are at. i will wait for the config.ini and we will compare those just incase. i imagine they will be identical and something else may be happening.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

I have the same issue. How were you able to resolve this problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:29 AM . Last Modified: ‎2024-03-19 01:28 AM

this thread is a few years old. lets make sure you are up to date on your firmware - AOS 3.7.3 and sy3p 3.7.2 if this is a symmetra 3 phase unit as well. also, what are your IM revisions?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of