Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2604:28 AM. Last Modified: 2024-03-1901:28 AM
Symmetra PX 40kW - what is the nominal voltage?
On August 8th our IT department supervised a full load test on a non-integrated system. The generator and ATS switch were purchased from different vendors and are not on the ISX Manager. The Symmetra 40 kw performed flawlessly. We learned that the generator also provides backup power for much of the building load, including the elevators. We had an electrician monitor power during the test.
He noted consistent 60 hz, but swells and sags when the elevator was used: high of 285 and low of 275.
He asked me the nominal voltage of the UPS. I'm not even certain I understand "nominal voltage."
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2604:28 AM. Last Modified: 2024-03-1901:28 AM
Hi Ed,
The nominal voltage is what the UPS will typically be running off of. The nominal for a PX 40K is 208 3PH but it can take an input voltage range for main operations of 177 - 240V.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2604:28 AM. Last Modified: 2024-03-1901:28 AM
Hi Ed,
The nominal voltage is what the UPS will typically be running off of. The nominal for a PX 40K is 208 3PH but it can take an input voltage range for main operations of 177 - 240V.