Shutting down 1 PC after exactly 2 minutes of UPS on battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutting down 1 PC after exactly 2 minutes of UPS on battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

0 Likes
5
3098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

Shutting down 1 PC after exactly 2 minutes of UPS on battery

Hi,

I'm trying to configure the PCBE in a way that if the UPS is on battery for 2 minutes, then my PC will shutdown (windows 10), I have another router and Ubuntu PC which I want them to run up until the UPS is out of battery capacity.

I set up PCBE in this order but it doesnt seem to work:

WWrb7w6ffGjckGhYtHoXGw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngWWrb7w6ffGjckGhYtHoXGw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Am I missing something? is that "red marked" configuration is about the remaining runtime and not a time on battery trigger ?

If so, then how can I make sure that my PC will shutdown after exactly after 2 mins of UPS on battery?

Please advise,

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

0 Likes
0
3097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

Hi,

You first need to install PCNS on each Windows 10 system. Then open the PCNS web interface on each system and select Configure Events. Under the heading of Configure Events you will see UPS on Battery. Click Shutdown, then check enable shutdown and enter 300 seconds for the delay and click Apply. PCNS will start the OS shutdown after the UPS has run on battery for 5 minutes. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

0 Likes
0
3097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

Hi Jacob,

You need to select the option " After the UPS has been on battery for" and set it to 120 seconds, this will make the PC to shutdown after the ups on battery for 2 mins but once the PC shutdowns the UPS also shutdown in few minutes and it waits for the power to return. PCBE software does not have the option to configure it to stay on once PC shutdowns hence it will shutdown disconnecting the power to the outlets. PowerChute network shutdown (PCNS) software have the option to set the UPS to stay on and for that, you need to go for the network management card since PCNS only communicates with the network card.

Regards,

Vinay

   You need to select the option " After the UPS has been on battery for" and set it to 120 seconds, this will make the PC to shutdown after the ups goes to on battery condition for 2 mins but once the PC shutsdown the UPS also will shutdown and wait for the power to return. PCBE software does not have the option to configure it to stay ON. Once the PC shutsdown it will shutdown disconnecting the power to the outlets. This option is only available in PowerChute network shutdown (PCNS) software and for that, you need to go for the network management card since PCNS only communicates with the network card. 
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

0 Likes
0
3097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

Vinay

Where can I find the settings for PCNS to shutdown 3 win10 PCs after 5 minutes once the Smart-UPS RT 5000 RM XL has switches over to battery to save battery energy to keep a voip phone on as long as it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

0 Likes
0
3098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:56 AM

Hi,

You first need to install PCNS on each Windows 10 system. Then open the PCNS web interface on each system and select Configure Events. Under the heading of Configure Events you will see UPS on Battery. Click Shutdown, then check enable shutdown and enter 300 seconds for the delay and click Apply. PCNS will start the OS shutdown after the UPS has run on battery for 5 minutes. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
3095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

Thank you much for the fast reply Bill, well appreciated, I will try these setting and let you know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
3096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

Thank so much Bill, the new settings work perfectly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore