Battery soft start fault after installing new battery - Smart-UPS X 3000
  • Battery soft start fault after installing new battery - Smart-UPS X 3000
Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM
5299
I am troubleshooting a Smart-UPS X 3000 (SMX3000RMLV2UNC). It gave the battery warning error so I ordered a new replacement #117 battery. After changing the battery I am getting the following errors:
  • At least one faulty battery exists.
  • A battery bus soft start fault exists.
  • An inverter fault exists.
  • In bypass in response to an internal hardware fault.
The inverter fault error started showing up after the battery replacement error but before I installed the new battery.
The UPS firmware is UPS 01.8 (ID10) and I have attached the /log/event.txt and /log/data.txt files.
What should I do to troubleshoot these problems? I do not want to power cycle the UPS if possible as there are production servers running on it.
event.txt.zip
data.txt.zip
  • battery_module_fault
  • fault
  • inverter
  • smartups_3000rmnet
This may require a replacement battery for the replacement battery you got..
I'd suggest with this one that you contact your local support to obtain that potential replacement as I am not aware of this issue not requiring something to be replaced at this time.
