Shutdown at Temperature = or > 100degrees

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown at Temperature = or > 100degrees
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

0 Likes
4
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

Shutdown at Temperature = or > 100degrees

Can anyone please share the setup steps to have servers connected to smart-ups 2000 automatically shutdown once
the temperature is equal to 100degrees, as well as send alerts at 90degrees. TY4A.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

0 Likes
0
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

Can anyone please share the setup steps to have servers connected to smart-ups 2000 automatically shutdown once
the temperature is equal to 100degrees, as well as send alerts at 90degrees. TY4A.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

0 Likes
0
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

Do you have a network management card with a temperature sensor?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

0 Likes
0
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

To be clear, not all network management cards have environmental monitoring - you need either an AP9619 or AP9631 card. Assuming you have one of those along with a temperature probe connected, you're good to go.

After logging in to the web interface, you should see a number of tabs at the top - you're interested in the "Environment" tab. Here you can configure the high/low & min/max temperature settings. Click on your sensor (either in the Overview section or Temp & Humidity) and configure your settings. The "Help" section is very helpful in case you have any questions - you can access it at the top right next to the "Log Off" button.

Once you've configured the settings to your liking, click on the "Administration" tab and go to the "Notification" sub-tab. Enter your email information in the "Email" subsections (server, recipients, test if you'd like) and then you can double check you'll receive email notifications for temperature events. To do this, click on "by event" under the "Event Actions" section, then on Temperature under Environment Events. Make sure email is enabled for those messages you'd like to receive.

In terms of shutting down your equipment when a threshold is exceeded, you will need to install [PowerChute Network Shutdown|http://www.apc.com/products/family/index.cfm?id=127] on your servers and tell the system to shutdown for different events in "Configure Events" (namely for "Environment: Temperature Probe 1 Out Of Range").

That should help get you started. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

0 Likes
0
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

Buzz - Thank you kindly for your response. The reason I was not seeing the option on the UPS/s is that we do not have a temperature probe installed.
Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:57 PM . Last Modified: β€Ž2024-03-07 02:16 AM

Can anyone please share the setup steps to have servers connected to smart-ups 2000 automatically shutdown once
the temperature is equal to 100degrees, as well as send alerts at 90degrees. TY4A.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore