Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:20 AM . Last Modified: 2024-03-12 11:42 PM
All,
With reference to my last post PowerChute is successfully work for environment Threshold reaches 30 Centigrade.
We also have configured low battery.
Now I am confused how can i dig out on which activity PowerChute Work 1) On Low Battery 2) High Temperature Threshold.
In my opinion Server Shutdown due to 2) High Temperature Threshold
Can Also guide me if i am correct Low Battery Threshold is 10%
All Screen Shots are attached
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:20 AM . Last Modified: 2024-03-12 11:42 PM
Hi,
PowerChute will trigger a shutdown based on your settings. You have configured "Temperature Probe 1 out of range" to trigger a shutdown so if the temperature is out of range a shutdown will occur. You have set the low battery threshold on the NMC to 2 minutes so if the runtime of the UPS falls below 2 minutes a signal will be sent to PowerChute and a shutdown will be triggered.
I recommend increase the low battery threshold to be a minimum of 2 minutes grater than the amount of time that is required to have the computer system/s power down gracefully.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:20 AM . Last Modified: 2024-03-12 11:42 PM
Hi,
PowerChute will trigger a shutdown based on your settings. You have configured "Temperature Probe 1 out of range" to trigger a shutdown so if the temperature is out of range a shutdown will occur. You have set the low battery threshold on the NMC to 2 minutes so if the runtime of the UPS falls below 2 minutes a signal will be sent to PowerChute and a shutdown will be triggered.
I recommend increase the low battery threshold to be a minimum of 2 minutes grater than the amount of time that is required to have the computer system/s power down gracefully.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.