Shutdown Hyper-V and VM configuration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown Hyper-V and VM configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
7
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

Shutdown Hyper-V and VM configuration

Hi all,
I have installed with success PowerChute Network Shutdown on my Hyper-V server.
On this Hyper-V server there are some virtual machine.

I have some doubt about PowerChute configuration on Hyper-V.
I would that when UPS is on battery and level is critical, VM start to shutdown and then Hyper-V server shutdown too.

I have found some setting on UPS side and PowerChute, but I am not totally sure about them.

On UPS I have seen that system can continue to running for about 30 minutes using UPS battery, so I have configured on UPS
Configuration > Shutdown Configuration >  Low Battery Duration = 20 minutes
Could it be fine?

After that on PowerChute I do not understand Runtime remaining below threshold in "Configure Events". Is it the time to shutdown the physical server? For example if my VM will shutdown in 5 minutes, I can set  Runtime remaining below threshold equal to 15 minutes?


Then I have enabled in Virtual
ization settings > VM Shutdown (ok) with VM Shutdown Duration = 360sec. (5 minutes).

Sorry, but it is my first experience about UPS configuration.

Thanks so much in advanced.
Federico

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:52 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:52 AM

Hello Bill,

thanks so much for your help.

Federico

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Hi,

Runtime remaining below threshold when set will trigger a shutdown when the UPS runtime fall below the set time while running on battery. If you hover over the i to the left of the event a pop up will appear explaining the event. 

gpZr9h%2BIK1k48qxwhfbFaQ%3D%3D.pnggpZr9h%2BIK1k48qxwhfbFaQ%3D%3D.png

The low battery duration will trigger a single to be sent to any PowerChute clients registered with the UPS. This is explained in Schneider Electric FAQ FA405707

Both settings are similar as they will trigger shutdown when the runtime falls below the set time. The difference is runtime remaining below threshold is set in the individual PowerChute client. Low battery duration is set on the NMC and will affect all registered PowerChute clients. 

 

On 4/2/2020 11:16 AM, Federico said:

After that on PowerChute I do not understand Runtime remaining below threshold in "Configure Events". Is it the time to shutdown the physical server? For example if my VM will shutdown in 5 minutes, I can set  Runtime remaining below threshold equal to 15 minutes?

If you configure runtime remaining at 15 minutes PowerChute will start the shutdown process when the UPS runtime falls below 15 minutes. The VMs will be commanded down, PowerChute will wait 5 minutes, then command the host down.

Since you configured low battery duration at 20 minutes that will occur first so the shutdown process will have begun prior to the 15 minute setting for runtime remaining. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Dear Bill,
thanks for your reply and sorry my late answare.

So a right configuration will be:

- Low battery trigger at 10 minutes (on UPS)
- Runtime remaining below threshold is set in the individual PowerChute client equal 20 minutes (on Hyper-V server)

I would that my VM will shutdown in the right way and than physical server will shut down.

Is right my answare about threshold configuration?
Thanks
Federico

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Hi,

On 4/9/2020 8:26 AM, Federico said:

- Low battery trigger at 10 minutes (on UPS)
- Runtime remaining below threshold is set in the individual PowerChute client equal 20 minutes (on Hyper-V server)

I would that my VM will shutdown in the right way and than physical server will shut down.

Yes. That will start the shutdown process when there is 20 minutes remaining of runtime. You should also configure the VM shutdown under the heading of virtualization setting in the PowerChute web interface. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Dear Bill,
thanks so for your reply and time.

Yes. That will start the shutdown process when there is 20 minutes remaining of runtime. You should also configure the VM shutdown under the heading of virtualization setting in the PowerChute web interface.

Are talking about the shutdown timer for VM?
In my case the value is 5 minutes.

Thanks so much
Federico

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:53 AM

Dear Bill,
thanks so much for your help.
This is my configuration (I hope that it is right):

9C5goZKQdThot6ihFe2nCg%3D%3D.png9C5goZKQdThot6ihFe2nCg%3D%3D.png

 

On PowerChute client (installed on Hyper-V Windows Server):

aFDgznBZntqOVysfjPqJCw%3D%3D.pngaFDgznBZntqOVysfjPqJCw%3D%3D.png

Elhk4wowmfG4YBs%2Fbb0wcg%3D%3D.pngElhk4wowmfG4YBs%2Fbb0wcg%3D%3D.png

Can say me if it is the right configuration?
Thanks so much
Federico

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:52 AM

0 Likes
0
3806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:52 AM

Hi,

On 4/14/2020 2:28 AM, Federico said:

Are talking about the shutdown timer for VM?
In my case the value is 5 minutes.

Yes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:52 AM

0 Likes
0
3807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:55 AM . Last Modified: ‎2024-03-08 03:52 AM

Hello Bill,

thanks so much for your help.

Federico

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore