SU1400NET

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU1400NET
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
7
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

SU1400NET

Hi guys,

OK it's old but still appears to be working normally - all tests pass including the brain-dead check. Our problem is as follows:

We replaced the battery this week, however when testing we are experiencing an un-expected behavior; after running on battery power and hitting the low-battery alarm, we then return to normal line power but the UPS will still power-cycle and re-set all connected equipment. Is this normal? Powerchute is running mostly default settings, this behavior is also occuring on a rack mounted version of this same UPS. We would expect (and would like) for the UPS when returning to line power even after a low battery alarm, to NOT terminate or inturrupt power delivery. Could this be because we are employing a command script to shut down other servers? Do we need to run a seperate script on resume of normal power? If so what would it look like?

Thanks,

Mark L

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

What software are you using? It looks like the software is ordering Windows to shut down and continue with shut down to guarantee 8 minutes after shut down process is initiated.

Do the outlets lose power when the power is returned without any software connected? If so, it's a hardware problem. If not, it's something in your software.

uptime wrote:
Here are our settings. Current runtime @ 52% load is 18 min on a full charge.

Time required for shutdown sequence: 8min
Low battery signal: 2min
Command file: Yes
Command file duration: 3min
OS shutdown delay: 5min
OS shutdown type: Shutdown
Enable OS reboot: Yes
UPS turnon battery capactity: 0%
UPS turnon delay: 0min

If we go on battery power for say 10min we cannot avoid a shutdown even when power comes back.

Message was edited by: uptime

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

i think if the UPS hits the low battery alarm, there is no way to stop the shutdown counter and the UPS needs to reboot. i have a couple of questions though.


•How much total runtime do you have?
•What is your low battery signal set to? (default is 2 min)


this situation i would suspect to be rare unless your settings are awkward and set incorrectly so im assuming you are doing this during a test? this shouldnt have anything to do with your scripts/command files.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

Hey winna,

Total runtime is around 18min @ 52% load. Low battery is indeed set to the 2 min default. It seems rather strange if it is in fact unavoidable for the UPS to power-cycle in this example. If line power returns why not stay up?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

under normal circumstances, yeah it should stay up but during the low battery duration is another story.

also, if you have powerchute network shutdown installed and those clients shutdown, they wont restart till the UPS is rebooted.

but if you pull the plug from the wall on the UPS and let it run for say, 5 minutes, and plug it back in, does it come back on correctly? or does it reboot in that scenario too?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Hi winna,

Yes it will continue the shutdown of the protected system. I've done this very test. I will note that it did enter the protected system shutdown sequence and was running our script. Never the less, the Protected system should not continue to shutdown on power resume imo. I also cannot find any setting that would control this behavior. What is the default action for an APC UPS in this circumstance? There is the 'Power Restored' action...do we need to run a command script for this event that would abort the shut-down? And if so, how or where can I get info on that?

Thanks in advance, I appreciate the help 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Here are our settings. Current runtime @ 52% load is 18 min on a full charge.

Time required for shutdown sequence: 8min
Low battery signal: 2min
Command file: Yes
Command file duration: 3min
OS shutdown delay: 5min
OS shutdown type: Shutdown
Enable OS reboot: Yes
UPS turnon battery capactity: 0%
UPS turnon delay: 0min

If we go on battery power for say 10min we cannot avoid a shutdown even when power comes back.

Message was edited by: uptime

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

Once a UPS starts its shutdown procedure, it will continue and shut itself off. The UPS itself knows it is doing a graceful turn off. There is no way to abort the graceful turn off once the UPS initiates it, even if the UPS gets utility back DURING the shutdown. Your best bet is to lower all of your delays so that the required time of shutdown sequence is lower, if possible

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

0 Likes
0
1422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:53 AM

What software are you using? It looks like the software is ordering Windows to shut down and continue with shut down to guarantee 8 minutes after shut down process is initiated.

Do the outlets lose power when the power is returned without any software connected? If so, it's a hardware problem. If not, it's something in your software.

uptime wrote:
Here are our settings. Current runtime @ 52% load is 18 min on a full charge.

Time required for shutdown sequence: 8min
Low battery signal: 2min
Command file: Yes
Command file duration: 3min
OS shutdown delay: 5min
OS shutdown type: Shutdown
Enable OS reboot: Yes
UPS turnon battery capactity: 0%
UPS turnon delay: 0min

If we go on battery power for say 10min we cannot avoid a shutdown even when power comes back.

Message was edited by: uptime

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore