Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Is it possible to set group 1 (controlled group) in SMT2200I in a way it won't turn on on its own? Ideally i'd like group 1 to behave this way:
if there's power outage:
if load on group 1 is low (eg. <10W) turn it off (means devices are already down, no time needed)
and never turn on again automatically even after power is back.
Can I do that? there's device in group 1 that misbehaves on power return and it needs to be watched by human when power returns and it's on / powers on because if peripherals turn on all at once it overloads power source blowing fuse and disconnecting power from UPS, so they need to be turned on one by one (so they need to be off and they can't get power back as they'd turn on automatically then)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Hi,
On 11/9/2017 7:56 AM, Damian said:Is it possible to set group 1 (controlled group) in SMT2200I in a way it won't turn on on its own?
Yes, if there is a network card installed in the SMT. If so go to Configuration - Outlet Groups and select Group1 and check "Stay off after power returns". When the outlet group is powered down when AC is restored the outlet group will remain off until switched on by a user.
On 11/9/2017 7:56 AM, Damian said:if load on group 1 is low (eg. <10W) turn it off (means devices are already down, no time neede
This feature is not available with the SMT.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Hi,
On 11/9/2017 7:56 AM, Damian said:Is it possible to set group 1 (controlled group) in SMT2200I in a way it won't turn on on its own?
Yes, if there is a network card installed in the SMT. If so go to Configuration - Outlet Groups and select Group1 and check "Stay off after power returns". When the outlet group is powered down when AC is restored the outlet group will remain off until switched on by a user.
On 11/9/2017 7:56 AM, Damian said:if load on group 1 is low (eg. <10W) turn it off (means devices are already down, no time neede
This feature is not available with the SMT.