Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Power Distribution Unit (PDPM)

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power Distribution Unit (PDPM)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:44 PM

0 Likes
10
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:44 PM

Power Distribution Unit (PDPM)

This question was originally posted by MUHAMMAD on APC forums on 11/13/2017


I have two different sites where APC Modular Power Distribution Units are Installed.

I am trying to read value of KW on SNMP protocol using OID  .1.3.6.1.4.1.318.1.1.22.4.3.1.0

I am getting value of KW on first site but at the other site using same procedure i am not getting data.

Any Idea why?

BR

Genjua

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by Angela on APC forums on 11/15/2017


Hi Genjua,

To clarify on #1, the model in the screenshot is the model of the network management module (unfortunately). Do you have any idea of the model/SKU of the actual PDPM - something like "PDPM277H" or "PDPM144F" perhaps?

Do other SNMP OIDs respond on the unit in Lahore? And is it just this specific value that won't respond? Or do NO SNMP OIDs work, like if you do an SNMP walk for example?

See Answer In Context

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by Angela on APC forums on 12/8/2017


Hi Genjua,

Sorry, I missed your previous message from a few weeks ago. I wish you a happy holidays too!

There is no way to restrict access to certain OIDs - you can only enable/disable SNMP or restrict access to ALL SNMP polling to certain IP addresses/IP ranges/hostnames. Have you compared the configuration between the units in regards to SNMP?

This is hard to answer 100% accurately without being able to see the problem and troubleshoot it live. 

You can extract the config.ini from each PDPM and I can look at the SNMP configuration if you want.

See Answer In Context

Reply
Share
Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by MUHAMMAD on APC forums on 11/13/2017


Angela 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by Angela on APC forums on 11/13/2017


What model of PDPM is this? What version of firmware is on it?

What specific response do you get to the power OID - is it 0, -1, or a timeout? I guess my question is, have you ruled out a general SNMP response problem vs. a problem with the device's configuration, set up, and specific value being missing for some reason.

I'd also see if this specific value is reporting correctly in the PDPM's web interface to compare.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by MUHAMMAD on APC forums on 11/14/2017


Good Day Angela,

Thanks much for your time. Please find the answer of your queries below:

  1. What model of PDPM is this? What version of firmware is on it?

See attached screen shots, Let me know if you need any further information on this point.

2. What specific response do you get to the power OID - is it 0, -1, or a timeout?

I am getting Bad Response timeout, Please see attached screen shots, PDU Islamabad is working fine and showing data, whereas PDU lahore is not showing data.

3. 'd also see if this specific value is reporting correctly in the PDPM's web interface to compare.

Yes, On Web Interface i am getting all the data correctly but having issue with SNMP.

Please asvise.

BR

Genjua

Attachments
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by Angela on APC forums on 11/15/2017


Hi Genjua,

To clarify on #1, the model in the screenshot is the model of the network management module (unfortunately). Do you have any idea of the model/SKU of the actual PDPM - something like "PDPM277H" or "PDPM144F" perhaps?

Do other SNMP OIDs respond on the unit in Lahore? And is it just this specific value that won't respond? Or do NO SNMP OIDs work, like if you do an SNMP walk for example?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by MUHAMMAD on APC forums on 11/16/2017


Good Day Angela, The model number is PDPM277H.

Yes, I am getting data from MIB Browser Walk Operation, But when i use OPC Server to fetch data i do not get all the data i get some current values and the rest KW KWH are BAD , Timeout.

It Seems that there is a firmware issue.....? What Do You Say?

BR

Genjua

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by Angela on APC forums on 11/20/2017


Hi Genjua,

if MIB browser works and OPC server does not, I would not guess a problem with firmware but rather OPC? Why do you suggest it is firmware based on OPC not working and MIB browser working? Because the other unit works fine? Is it possible there is a configuration problem for this IP address/agent in OPC?

Also FYI, I will be away this week due to US Thanksgiving holiday break. If you need urgent support on this matter, I suggest to contact your local technical support office. Otherwise, I will get back to you as soon as I am able and back from holiday.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by MUHAMMAD on APC forums on 11/20/2017


Good Day Angela,

My Point is same OPC Server with Same Configuration on the other site is working perfectly fine, That means something is wrong in PDU Configuration or Firmware.

I wish you a very happy holidays.

BR

Genjua

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by MUHAMMAD on APC forums on 12/8/2017


Angela Please confirm that is there is any way in PDPM configuration that someone use it to restrict data to share over SNMP? for example they share PDPM Current Values Over SNMP and restrict KW & KWH Values Over SNMP?

BR

Genjua

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by Angela on APC forums on 12/8/2017


Hi Genjua,

Sorry, I missed your previous message from a few weeks ago. I wish you a happy holidays too!

There is no way to restrict access to certain OIDs - you can only enable/disable SNMP or restrict access to ALL SNMP polling to certain IP addresses/IP ranges/hostnames. Have you compared the configuration between the units in regards to SNMP?

This is hard to answer 100% accurately without being able to see the problem and troubleshoot it live. 

You can extract the config.ini from each PDPM and I can look at the SNMP configuration if you want.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 11:45 PM

This reply was originally posted by MUHAMMAD on APC forums on 12/30/2017


Angela Good Day,

The problem has been resolved thanks much for the support.

I have heard that there was a problem in cat6 connections and also our power department perform some setting on PDPM.

Thanks Much Once Again!!

BR

Genjua

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc