SmartUPS 700: new batteries, no runtime

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 700: new batteries, no runtime
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:45 PM

0 Likes
3
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:45 PM

SmartUPS 700: new batteries, no runtime

Hi folks,

A bunch of questions, some of which are partially answered elsewhere/answered for other equipment; sorry for the repetition.

I recently picked up a used SmartUPS 700 (DL700; 50.14.D) with the understanding that the batteries supported no runtime and replaced the batteries with fresh. Unfortunately, even after self-testing and waiting until the NMC (AP9617 rev. A10) reports 100% battery charge, runtime calibration reports 0 minutes. I've tried this several times, each time getting the "0 minutes" result, with the NMC reporting that the batteries are discharged.

The intertubes seem to indicate that the battery constant needs to be reset. Is there any way (which I haven't found yet) to do this via the NMC, or do I truly have to cobble together all the ancient serial bits?

If the latter: I have a 940-0127B, a 940-0144A, an RJ45-to-DB9 adapter (pinout unknown), a regular DB9 serial, and a null modem cable. Any chance I can make this work w/o hunting down another cable? If not: Which part number do I need? And are these instructions correct for this unit? https://web.archive.org/web/20130808070735/http://www.joeteck.com/apc-repair.htm

Any advice will be appreciated.

Cheers,

-sth

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

Thanks, Vinay. I've contacted support and Jan says a calibration key is on its way. Great customer service, all around.

Cheers,

-sth

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

Hi Sam,

We do not recommend entering battery constant value. We have come across an issue where entering a wrong value has caused the UPS damage. So APC stopped providing the battery constant value. However, we do have the calibration key for this unit to calibrate the runtime. You can request the calibration key from the customer support. They will help you out to ship one for you.

Regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

You can reach them on 800-555-2725

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:45 PM . Last Modified: ‎2024-02-29 11:38 PM

Thanks, Vinay. I've contacted support and Jan says a calibration key is on its way. Great customer service, all around.

Cheers,

-sth

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore