Servers are not turning on after power outage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Servers are not turning on after power outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
118
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
4
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Servers are not turning on after power outage

Hello!

I have a problem that during a long power outage my servers are not starting up automatically when the power comes back. My cabling can be seen in the attached image file. The servers have 2 power cordes. 1 cord is connected to a UPS with NMC card installed and manage the shutdown events. The other cord is connected to a different UPS, but that one has no NMC card installed.

I am suspecting that the problem can be that the UPS with no NMC did not drain all the batteries and one of the server PSU did not realized a missing input power event. Is this possible to happen?

I have the following APC's:
APC Matrix-UPS 5kVA (No NMC installed)
SMT3000I (with NMC)
SURTD3000XLI (with NMC)

As far as I understand the Matrix UPS and the others are from different model family and I may not be able to configure a rendundant UPS setup even if I install an NMC in the Matrix UPS.

What are my option here to achieve my goal that the servers can start up automatically.

Thank you,
PG

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Hi,

Yes. The Matrix in compatible with the NMC. I do suggest test first before purchasing a new card. You can pull a card from one of the other Smart-UPS and insert it in the Matrix. Test the configuration and if all goes well then purchase a new NMC. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Hi,

The official answer is the UPS are not of the same family and therefore not compatible.

The unofficial answer is

  1. Install PCNS and configure for a single UPS.
  2. Stop the PowerChute Service.
  3. Edit the pcnsconfig.ini file and add a second UPS to the Network Management Card section. See example below.
  4. Change enrolWithNMC = false
  5. If not done in the initial configuration in the Shutdown setting set turnoffUps = true
  6. Restart the PowerChute Service.
  7. Log into each NMC and add the PCNS client to the PowerChute client list.

[NetworkManagementCard]
mode = redundant
IP_1 = 10.0.0.250
port = 80
protocol = http
enrolWithNMC = false
acceptCerts = false
IP_2 = 10.0.0.251

PowerChute will then listen to each NMC and react as configured for redundant UPS even though they are of different families. 

NOTE: The Matrix must have firmware Y or Z to be compatible with NMC. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Tank you for your answer, we will try out your solution, if indeed our apc setup is the reason for the servers not starting up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Hello,

We have the following Matrix UPS:
mx5000eu
Display Rev.: 3Z
UPS FW rev: 5ZI

Is this model compatible with you unofficial solution?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Hi,

Yes. The Matrix in compatible with the NMC. I do suggest test first before purchasing a new card. You can pull a card from one of the other Smart-UPS and insert it in the Matrix. Test the configuration and if all goes well then purchase a new NMC. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of