Certificate management with Linux or Mac

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Certificate management with Linux or Mac
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
8
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

Certificate management with Linux or Mac

Is there a way to perform certificate management for the NMC2 using Linux or Mac? We do not have any Windows systems.

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • management
  • nmc2
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Thank you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

I'm going to guess silence means "no"... is there any way to raise this as an issue with  APC/ Schneider?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

Hi,

If you are asking about a Security Wizard then the answer is no. We do not offer a wizard for Mac or Linux. You can however use one of the many online CA - SSL certificate tools to create a certificate and upload that certificate to the NMC.  Information on how to upload the file will be found on page 14 of the NMC security handbook.  

https://www.apc.com/salestools/LFLG-9VYK3D/LFLG-9VYK3D_R1_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

So, a few quick questions...

I know of many SSL certificate tools, but don't know of any that work with PKCS#15. Can you post some example links?

Do any of these certificate tools prepend the custom header to the p15 files that APC requires?

Also, doesn't what you suggest require sending both the certificate and associated private key to a host on the internet that is outside our control? Security folk would consider sending the private key to a random server a Bad Idea.

Thanks,

Denny

 

Reply

Link copied. Please paste this link to share this article on your social media post.

dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

???

Reply

Link copied. Please paste this link to share this article on your social media post.

dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

Any additional guidance you can provide on this? Any way to accomplish secure certificate based  connectivity using Linux or Mac?

Reply

Link copied. Please paste this link to share this article on your social media post.

dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

It seems that there is no current way to accomplish this. I would like to file an enhancement request to either provide the existing APC software on Linux, or (preferably) to allow the NMC2 to import certificates in a more commonly used format (PKCS#12 for instance). How do I file that enhancement request?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:38 AM

Hi,

I will enter a request on your behalf. 

Reply

Link copied. Please paste this link to share this article on your social media post.

dennypage
Crewman dennypage
Crewman

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

0 Likes
0
1779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:00 AM . Last Modified: ‎2024-03-08 04:38 AM

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore