Hello,
My environment is
2 Esxi Vmware hosts 6.5 with HA
1 Vcenter on VM on the HA cluster.
1 APC Smart-UPS 3000 XLM
Settings :
I set the APC management card
I installed the APC Vmware appliance and set the Powerchuteclient
In these settings I set the VM Prioritization with "VM shutdown Duration"
My question are :
When the APC is on battery, When is launched the VMs shutdown sequence ? I suppose I can set the battery
I mean, when is laucnhed the VM shutdown sequence.
Thank you very much by advance.
Laurent
I set the network card management
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:59 AM . Last Modified: 2024-03-08 04:39 AM
Hi,
I recommend increasing the low battery duration to be 2 minutes greater than the time needed to power the systems down and bring them back on line. This is a fail safe as the UPS should not reach low battery since the systems would be off prior to that happening.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:58 AM . Last Modified: 2024-03-08 04:39 AM
Hi,
PCNS will start the shutdown sequence based on the events. When a shutdown action is enabled for an event, PowerChute treats the event as critical and will trigger a shutdown sequence. Events to trigger a shutdown will be found in the PCNS web interface under the heading of Configure Events. Shutdown is not supported for all events: this is indicated by the presence or absence of an icon on the event row. The Delay field is the amount of time in seconds that PowerChute should wait before initiating the shutdown sequence. By default, the On Battery event has a delay of 120 seconds, whereas the default for all other events is 0 seconds.
By default, PowerChute will only trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. Shutdown cannot be disabled for these events using the PowerChute user interface.
This screenshot shows the On battery event
After selecting Shutdown in the next screen I has configured a delay of 300 seconds (5 minute).
What will happen is after the UPS has run on battery for 300 seconds PowerChute will start the shutdown process.
I recommend you read the User's Guide. Sample shutdown scenarios are discussed starting on page 100. Configurable events are discussed starting on page 144
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:59 AM . Last Modified: 2024-03-08 04:39 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:59 AM . Last Modified: 2024-03-08 04:39 AM
Hi,
I recommend increasing the low battery duration to be 2 minutes greater than the time needed to power the systems down and bring them back on line. This is a fail safe as the UPS should not reach low battery since the systems would be off prior to that happening.
Link copied. Please paste this link to share this article on your social media post.