When is started the Vmware VMs Shutdown ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • When is started the Vmware VMs Shutdown ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
3
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

When is started the Vmware VMs Shutdown ?

Hello,

My environment is

2 Esxi Vmware hosts 6.5 with HA

1 Vcenter on VM on the HA cluster.

1 APC Smart-UPS 3000 XLM

Settings :

I set the APC management card 

I installed the APC Vmware appliance and set the Powerchuteclient

In these settings I set the VM Prioritization with "VM shutdown Duration"

My question are :

When the APC is on battery, When is launched the VMs shutdown sequence ? I suppose I can set the battery

I mean, when is laucnhed the VM shutdown sequence. 

Thank you very much by advance.

Laurent

 

 

I set the network card management

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

Hi,

I recommend increasing the low battery duration to be 2 minutes greater than the time needed to power the systems down and bring them back on line. This is a fail safe as the UPS should not reach low battery since the systems would be off prior to that happening. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

Hi,

PCNS will start the shutdown sequence based on the events. When a shutdown action is enabled for an event, PowerChute treats the event as critical and will trigger a shutdown sequence. Events to trigger a shutdown will be found in the PCNS web interface under the heading of Configure Events.  Shutdown is not supported for all events: this is indicated by the presence or absence of an icon on the event row. The Delay field is the amount of time in seconds that PowerChute should wait before initiating the shutdown sequence. By default, the On Battery event has a delay of 120 seconds, whereas the default for all other events is 0 seconds.

By default, PowerChute will only trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. Shutdown cannot be disabled for these events using the PowerChute user interface.

This screenshot shows the On battery event

oMS7I8VsMqVFPwBAE1ogug%3D%3D.pngoMS7I8VsMqVFPwBAE1ogug%3D%3D.png

After selecting Shutdown in the next screen I has configured a delay of 300 seconds (5 minute).

TAVJPR7uV%2BjyWYSEe4CcaA%3D%3D.pngTAVJPR7uV%2BjyWYSEe4CcaA%3D%3D.png

What will happen is after the UPS has run on battery for 300 seconds PowerChute will start the shutdown process.

I recommend you read the User's Guide. Sample shutdown scenarios are discussed starting on page 100. Configurable events are discussed starting on page 144 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

Hello and thank you for your answer !

I set the "UPS on battery" event on 360s.

On the "UPS Network Management Card" software, do I need set something ? or I can let the default settings ?

mDodvx4qsvtuwPdVr4OLhg%3D%3D.pngmDodvx4qsvtuwPdVr4OLhg%3D%3D.png

Thank you

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
1143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:59 AM . Last Modified: ‎2024-03-08 04:39 AM

Hi,

I recommend increasing the low battery duration to be 2 minutes greater than the time needed to power the systems down and bring them back on line. This is a fail safe as the UPS should not reach low battery since the systems would be off prior to that happening. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of