File transfer to/from an NMC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • File transfer to/from an NMC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
2
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

File transfer to/from an NMC

I have a Symmetra PX with an Network Management Card running application module px2 v3.7.7 and AOS v3.9.0.  I can connect and login to FTP on the NMC, using the Windows command-line FTP client, but whenever I issue an "ls" or "get config.ini" command it just hangs on "about to open data connection" and eventually times out.

I have also tried SCP.  That also fails after a long delay.

I want to get the config.ini file for upload to a replacement card.  This one has been mysteriously restarting every couple of days, so we ordered a replacement part.  I'd really like to avoid figuring out how to configure all the settings from scratch.  And ideas why I can't download the config.ini file?

220 0G-9354 Network Management Card AOS v3.9.0 FTP server ready.
User (main_ups-ccc.mda.ca:(none)): apc
331 User name okay, need password.
Password:
230 User logged in, proceed.
ftp> ls
200 PORT Command okay.
150 File status okay; about to open data connection.

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
2743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

Hi Carlo,

It's possible that the FTP data port is blocked - the NMC uses port 21 as the server, but port 20 to actually transfer files. Could there be a software firewall blocking ports between your PC and the NMC? Could you perhaps make a direct network connection between the NMC and a computer?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

Hi Carlo,

It's possible that the FTP data port is blocked - the NMC uses port 21 as the server, but port 20 to actually transfer files. Could there be a software firewall blocking ports between your PC and the NMC? Could you perhaps make a direct network connection between the NMC and a computer?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

0 Likes
0
2743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:58 AM . Last Modified: ‎2024-03-08 04:39 AM

This was an obvious possibility that I had written off because there is no firewall between my PC and the UPS NMC, and the Windows firewall is turned off on my PC.  But your question made me think about the Checkpoint endpoint security.  And yes, it turns out it's the Checkpoint endpoint security blocking the high-port-number data connection from the NMC back to my PC.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore