Serial Communication with APC UPS RM 750 (SMT750RMI2U)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Serial Communication with APC UPS RM 750 (SMT750RMI2U)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
esekh_apc
Crewman esekh_apc
Crewman

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

0 Likes
4
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

Serial Communication with APC UPS RM 750 (SMT750RMI2U)

Try connect to  APC UPS  RM 750 (SMT750RMI2U) via serial interface and cable that was with device 940-625A. Used real COM1 port where OK work early old my UPS SMART 1000.

I try to use software:

  • PowerChute Business 9.2.
  • APCUPSD
  • PLINK for direct connect to com1

But device not detected. COM Port not answer.

By post :

http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/12876/serial-communication-wi...

I have information that SMT750 should work with serial port in any case.

When i test to use with USB  connection  PowerChute  Business  9.2 detect ups OK .

I manual described that can work or serial or USB  connection in one time. May be need switch by some procedure ? 

Factory reset not help in my case.

SN: AS1621241318

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • rs232
  • serial
  • smt750
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

Hello,

What software are you trying to connect to the the UPS over serial comm? If anything other than PowerChute Business Edition it is not supported. If PowerChute Business Edition is failing to discover the UPS over serial comm what version of PowerChute are you installing? 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
esekh_apc
Crewman esekh_apc
Crewman

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

Thanks for SerialTerm.exe. By this apps I detected wrong MB cable connector. They was with other order of pins.
And now I know that new SMART-UPS use SPEED 9600.8.n.1.n,  with old SMART-UPS used speed 2400.8.n.1.n

At image show order of pins.

But now other problem with start Agent.

After many reinstall of program agent 9.2, now not started service of PowerChute Business Edition Agent.

7024 Error Microsoft-Windows-Service Control Manager System 03.03.2017 4:20:05

The APC PBE Agent service terminated with the following service-specific error: The operation completed successfully.

101 Error APCPBEAgent Application 03.03.2017 4:20:04

Error: 0, Time out 90 seconds. Service start operation canceled.

But early at this host agent started correctly.

It  link not resolve same problem.

Server Core HV-2016. USB connection. APC UPS RM 750.

Logs: pcbe.log

2017-03-02 19:41:26,108 [main] INFO - [application.PicardApplication] - Legacy logging adapter enabled.
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] Java Runtime: Java(TM) SE Runtime Environment (ve
rsion: 1.8.0_31)
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] Java Home: C:\PROGRA~2\APC\POWERC~1\JRE18~1.0_3
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] JVM: Java HotSpot(TM) Client VM (version: 25.31-b
07)
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] OS: Windows Server 2012 (x86)
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] Time Zone: Europe/Helsinki
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] PCBE dir: C:\PROGRA~2\APC\POWERC~1\agent
2017-03-02 19:41:26,124 [main] ERROR - [application.PicardApplication] Can not read M11.cfg file:
java.io.FileNotFoundException: m11.cfg (The system cannot find the file specified)
at java.io.FileInputStream.open(Native Method)
at java.io.FileInputStream.(Unknown Source)
at java.io.FileInputStream.(Unknown Source)
at com.apcc.m11.application.PicardApplication.verifyAndUpdateConfigFile(Unknown Source)
at com.apcc.m11.application.PicardApplication.createPermanentStorage(Unknown Source)
at com.apcc.m11.application.PicardApplication.main(Unknown Source)
2017-03-02 19:41:26,124 [main] INFO - [application.PicardApplication] Created thePermanentStorage
2017-03-02 19:41:26,139 [PcbeHSM-EventDispatcher] INFO - [AgentHSM.AgentHsm] State Change InitialState -> ActiveState
2017-03-02 19:41:27,155 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:28,171 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:29,188 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:30,204 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:31,220 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:32,235 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:33,252 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:34,268 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false
2017-03-02 19:41:35,283 [main] INFO - [application.PicardApplication] isStartupComplete() - returns: false

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

esekh_apc
Crewman esekh_apc
Crewman

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

I do it recommendation for clear:

http://www.apc.com/us/en/faqs/index?page=content&id=FA159894&actp=search&viewlocale=en_US&searchid=1...

And after reinstall now all ok.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

Hello, can u help me? My smt750i can`t connect with my PC over serial port, but ur program showing this.vi6jztiRE8UFG7TpJvmgiA%3D%3D.pngvi6jztiRE8UFG7TpJvmgiA%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

0 Likes
0
2500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:45 AM . Last Modified: ‎2024-03-18 03:17 AM

Hello,

What software are you trying to connect to the the UPS over serial comm? If anything other than PowerChute Business Edition it is not supported. If PowerChute Business Edition is failing to discover the UPS over serial comm what version of PowerChute are you installing? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of