Dear All
I'm facing a Critical Event (distorted waveform. 0x020F) in Smart-UPS SRT 8000 (SRT8KRMXLI). When the the Power supply is from specific MotoGenerator. The UPS is going to swich off the Outlet Group and all devices connected are facing unexpected shutdown.
Attached you can find logs and the configuration .
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:17 AM
Hi Hector,
Sorry about the late response, but can you get me the complete logs, you can get this from the web interface - ABOUT > SUPPORT > GENERATE LOGS, once you have the logs, I'd like to take a look at the config.ini.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Checking on your configuration, your unit is setup to output 230V, and input the voltage you're getting is about 220Vs. the load you have attached on the UPS are they set for what voltage? The input and output voltage should be about the same so that if the UPS goes on bypass, the load attached to it won't get damage.
you can also refer to - http://www.apc.com/us/en/faqs/index?page=content&id=FA157068
Regards
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Hi Merick
All devices connected to both UPS can work with 220-240 V. Could you advice with your recommendation in order to solve this issue
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Hey Hector,
Under configuration > Power Settings > Rated Output Voltage
if you have an option for 220v, select that, now before you change the output voltage the UPS should be on stand by.
Regards
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
Hi Merick
I will proceed with one UPS and we can check the performance
Regards
Hector
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:46 AM . Last Modified: 2024-03-18 03:16 AM
dear Hector,
change the input settings not output settings .
thanks
Link copied. Please paste this link to share this article on your social media post.