Sensor communication lost

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Sensor communication lost
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
7
3462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

Sensor communication lost

Hi Everyone,

Randomly i'm seeing this error and email alerts are being generated from two of my APC's.

Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Integrated at Int Sensor Loc) communication.

Any idea what the issue is and how to resolve this?

Here are some environment details:

Model Number: AP9619
APC OS: 3.7.3
Application Module: 3.7.2
Hardware Revision: A10

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apc
  • communication
  • network_management_card
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

For me it helped to reset temperature sensors, there was a phantom sensor in the list. After the reset it has disappeared.

Go to Administration->General->Reset->Reset only, check "Lost Environmental Communication Alarms"

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

oh and i forgot to ask - do you have a temperate probe attached to the management card (it plugs into a PS/2 style type of connector).

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

Hi,

Thanks for your help.
I've attached the files as requested. We do not have the probes attached to the device. It's just a random occurrence.

Removed IP info.

Message was edited by: helpdesk@zadv.com

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

it is normal to see that after a warmstart. a warmstart is a reboot of the network management card's management interface so after that happens, everything re-initializes and restores communication. a warmstart can occur for [these reasons|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2572].

i only saw this error once at the top of this log? is that right?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

Hi,

i'm having a similar issue, except it's filling up my logs. Here is the hardware i have and below it a sample of the logs. I have nothing connected to the probe connector:

Model: Smart-UPS 1500
Serial Number: AS0532122102
Firmware Revision: 653.12.I
Manufacture Date: 08/06/05

Hardware Factory

Model Number: AP9619
Serial Number: BA0941025628
Hardware Revision: A10
Manufacture Date: 10/08/2009
Management Uptime: 0 Days 3 Hours 34 Minutes

Application Module

Name: sumx
Version: v3.5.8
Date: 11/05/2008
Time: 15:08:57

APC OS (AOS)

Name: aos
Version: v3.6.1
Date: 08/13/2008
Time: 18:49:49




19:59:43 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
19:59:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:00:03 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:00:13 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:00:23 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:00:33 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:00:43 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:00:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:03 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:13 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:23 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:33 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:43 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

for your issue, what I would do is uninstall the network management card from your UPS and when you look at the PCB boards, there are actually two that form the card. there is a large white connector that holds them together. i would reseat this connection and ensure it is secure. once you do this, reinstall the card and see if the messages still persist. i'd also note that you are one firmware revision behind if you wanted to upgrade. i don't think it will fix the issue here or is related to it but i figured i'd mention it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

Hi Everyone,

Randomly i'm seeing this error and email alerts are being generated from two of my APC's.

Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Integrated at Int Sensor Loc) communication.

Any idea what the issue is and how to resolve this?

Here are some environment details:

Model Number: AP9619
APC OS: 3.7.3
Application Module: 3.7.2
Hardware Revision: A10

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

0 Likes
0
3463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:40 PM . Last Modified: ‎2024-03-07 02:05 AM

For me it helped to reset temperature sensors, there was a phantom sensor in the list. After the reset it has disappeared.

Go to Administration->General->Reset->Reset only, check "Lost Environmental Communication Alarms"

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore