Hi Everyone,
Randomly i'm seeing this error and email alerts are being generated from two of my APC's.
Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Integrated at Int Sensor Loc) communication.
Any idea what the issue is and how to resolve this?
Here are some environment details:
Model Number: AP9619
APC OS: 3.7.3
Application Module: 3.7.2
Hardware Revision: A10
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
For me it helped to reset temperature sensors, there was a phantom sensor in the list. After the reset it has disappeared.
Go to Administration->General->Reset->Reset only, check "Lost Environmental Communication Alarms"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
oh and i forgot to ask - do you have a temperate probe attached to the management card (it plugs into a PS/2 style type of connector).
thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
it is normal to see that after a warmstart. a warmstart is a reboot of the network management card's management interface so after that happens, everything re-initializes and restores communication. a warmstart can occur for [these reasons|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2572].
i only saw this error once at the top of this log? is that right?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
Hi,
i'm having a similar issue, except it's filling up my logs. Here is the hardware i have and below it a sample of the logs. I have nothing connected to the probe connector:
Model: Smart-UPS 1500
Serial Number: AS0532122102
Firmware Revision: 653.12.I
Manufacture Date: 08/06/05
Hardware Factory
Model Number: AP9619
Serial Number: BA0941025628
Hardware Revision: A10
Manufacture Date: 10/08/2009
Management Uptime: 0 Days 3 Hours 34 Minutes
Application Module
Name: sumx
Version: v3.5.8
Date: 11/05/2008
Time: 15:08:57
APC OS (AOS)
Name: aos
Version: v3.6.1
Date: 08/13/2008
Time: 18:49:49
19:59:43 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
19:59:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:00:03 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:00:13 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:00:23 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:00:33 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:00:43 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:00:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:03 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:13 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:23 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:33 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:43 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
20:01:53 Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0345
20:01:53 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Temperature Sensor at 0513-1E) communication. 0x0344
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
for your issue, what I would do is uninstall the network management card from your UPS and when you look at the PCB boards, there are actually two that form the card. there is a large white connector that holds them together. i would reseat this connection and ensure it is secure. once you do this, reinstall the card and see if the messages still persist. i'd also note that you are one firmware revision behind if you wanted to upgrade. i don't think it will fix the issue here or is related to it but i figured i'd mention it.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
Hi Everyone,
Randomly i'm seeing this error and email alerts are being generated from two of my APC's.
Environment: Lost the local network management interface-to-integrated Environmental Monitor Input T Sensor (Integrated at Int Sensor Loc) communication.
Any idea what the issue is and how to resolve this?
Here are some environment details:
Model Number: AP9619
APC OS: 3.7.3
Application Module: 3.7.2
Hardware Revision: A10
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:40 PM . Last Modified: 2024-03-07 02:05 AM
For me it helped to reset temperature sensors, there was a phantom sensor in the list. After the reset it has disappeared.
Go to Administration->General->Reset->Reset only, check "Lost Environmental Communication Alarms"