APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
I have search but didnt find the answer, can i change sensitivity setting when there is load on it. Live severs...
thanks!
Patrick
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
Hi,
On 4/23/2019 7:19 PM, Patrick said:I have search but didnt find the answer, can i change sensitivity setting when there is load on it. Live severs...
Yes you can. Changing the sensitivity will not cause an output disruption.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
Hi,
On 4/23/2019 7:19 PM, Patrick said:I have search but didnt find the answer, can i change sensitivity setting when there is load on it. Live severs...
Yes you can. Changing the sensitivity will not cause an output disruption.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
Thank you!
Can i ask another, Should i do a calibration test and is it ok to do this live?
I'm very noob with this!
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 AM . Last Modified: 2024-03-15 06:03 AM
Hi,
If the UPS is new there is no need to run a calibration test. You should run a calibration test if you see that the available runtime is lower than expected based on the load or if you have replaced the battery.
To answer the question, yes you can run a calibration test with the load powered on. When running a calibration test the system requires a load of 30% or greater and the battery to be 100% charged to calculate the run time accurately.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.