Recently had a pretty serious failure of an APC 3000 UPS that almost started a fire

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Recently had a pretty serious failure of an APC 3000 UPS that almost started a fire
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
2
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

Recently had a pretty serious failure of an APC 3000 UPS that almost started a fire

We are a firm believer in protecting our computer equipment with APC UPS units.  We have always replaced our battery packs on time with OEM battery packs and have generally had great experience with these units.  This past Saturday, however, a 3000 unit that was installed in our 100+ year old City Hall building failed rather catastrophically and thankfully did not fully catch fire.  When I arrived onsite, the unit had every single LED flashing on the front panel and you could see carbon tracking out of most of the side vents.  The unit was not beeping, was not overly warm and no outlets had tripped.  The site wiring light was not lit and plugged in equipment was still fully functional.  While the local fire department was on site, we attempted to power off the unit so they could safely unplug it.  It immediately let out a "bzzzzzzzzz" sound along with a loud crack and a fairly scary electrical arc.  There was smoke coming from the back of the unit out of the rear vents and it had a very acrid odor to it.  It clearly smelled of an electrical fire and the fire staff had me remove the battery pack.  The batteries all appeared to be in good shape and had recently been refreshed and all was normal.  When I opened the unit, however, you could clearly see that it was FULL of carbon and soot and there were some caps and other items onboard that were completely melted.  The inside is almost entirely black from the fault and you could see it had been "simmering" for quite some time.  Thankfully, no fire was created and I'm thankful some on duty police officers reported the smell of electrical fire so we saved the building.  Can someone from Schneider or the community offer any insight as to what happened?  

The numbers on the back of this particular unit are:  DLA3000RM2U  JS0617004980

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

Hi, 

The flashing LEDs may indicate relay weld failure. The arcing and smell was probably emitted from the power inverter circuit which was destroyed due to the failure, possibly at some point when the unit conducted self test or responded to a power failure. Wether there was any other issue behind this (eg. drying out of electrolytic capacitors), I can't tell. If you are working with 10+ year old units, it is best to refurbish them in a professional service center to avoid failure caused by aging components inside the circuit. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

Hi Marc

I'm sorry to hear about your experience with one of our units. We take the safety aspect of our products extremely seriously and as such ask if you could contact our customer care team (Tel: 800-555-2725 or webchat https://www.apc.com/us/en/tools/chat/ )and they can start the process to investigate how this issue occurred. 

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 AM . Last Modified: ‎2024-03-15 06:02 AM

Hi, 

The flashing LEDs may indicate relay weld failure. The arcing and smell was probably emitted from the power inverter circuit which was destroyed due to the failure, possibly at some point when the unit conducted self test or responded to a power failure. Wether there was any other issue behind this (eg. drying out of electrolytic capacitors), I can't tell. If you are working with 10+ year old units, it is best to refurbish them in a professional service center to avoid failure caused by aging components inside the circuit. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore