The session is not authenticated show on error.log on PCNS 4.3 with Vcentre & ESXi 6.0

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The session is not authenticated show on error.log on PCNS 4.3 with Vcentre & ESXi 6.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:11 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
1
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:11 AM . Last Modified: ‎2024-03-15 06:02 AM

The session is not authenticated show on error.log on PCNS 4.3 with Vcentre & ESXi 6.0

Dear Support,

As client deploy the PCNS 4.3 without AD domain. So, we create the local account on Vcentre and ESXi host server. 

The error log show as following:

2019-04-23T21:31:59,833 ERROR Thread-1 com.vmware.vim25.ws.WSClient java.net.SocketTimeoutException: connect timed out
at java.base/java.net.PlainSocketImpl.waitForConnect(Native Method) - Exception caught while invoking method: RetrieveProperties
2019-04-23T21:32:09,834 ERROR Thread-1 com.vmware.vim25.ws.WSClient java.net.SocketTimeoutException: connect timed out
at java.base/java.net.PlainSocketImpl.waitForConnect(Native Method) - Exception caught while invoking method: Logout
2019-04-23T21:32:09,834 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - isValidServiceInstance() - unable to connect to vCenter host: 10.13.248.70 - java.rmi.RemoteException: Exception caught trying to invoke method RetrieveProperties; nested exception is: 
java.net.SocketTimeoutException: connect timed out
2019-04-23T21:32:19,871 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:32:29,919 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:32:30,857 ERROR pool-72-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:32:40,921 ERROR pool-73-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:33:09,978 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:33:20,026 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:33:20,979 ERROR pool-74-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:33:31,028 ERROR pool-75-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:34:00,080 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:34:10,112 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:34:11,081 ERROR pool-76-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:34:21,129 ERROR pool-77-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:34:50,198 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:35:00,246 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:35:01,199 ERROR pool-78-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:35:11,247 ERROR pool-79-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:35:40,314 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:35:50,349 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:35:51,318 ERROR pool-80-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:36:01,350 ERROR pool-81-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:36:30,420 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:36:40,468 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:36:41,421 ERROR pool-82-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:36:51,471 ERROR pool-83-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:37:20,533 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:37:30,566 ERROR qtp1178594393-184 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:37:31,534 ERROR pool-84-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:37:40,629 ERROR Thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:37:41,567 ERROR pool-85-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:37:50,663 ERROR qtp1178594393-184 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - getVCenterServerConnection() - timed out while trying to establish a connection to vCenter: 10.13.248.70
2019-04-23T21:37:51,632 ERROR pool-86-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:38:01,664 ERROR pool-87-thread-1 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
2019-04-23T21:38:04,477 ERROR pool-70-thread-1 com.vmware.vim25.ws.WSClient com.vmware.vim25.NotAuthenticated: The session is not authenticated.
at java.base/jdk.internal.reflect.NativeConstructorAccessorImpl.newInstance0(Native Method) - Exception caught while invoking method: CurrentTime
2019-04-23T21:38:04,477 ERROR pool-70-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection  - validateESXiConnection() - host: wch-MSVM01 - The session is not authenticated., attempting reconnection
2019-04-23T21:38:04,477 ERROR pool-70-thread-1 com.vmware.vim25.ws.WSClient com.vmware.vim25.NotAuthenticated: The session is not authenticated.
at java.base/jdk.internal.reflect.NativeConstructorAccessorImpl.newInstance0(Native Method) - Exception caught while invoking method: Logout
2019-04-23T21:38:04,680 ERROR pool-70-thread-1 com.apcc.m11.components.Shutdowner.ExecuteSupportedVirtualizationFeatures  - logEnterMaintenanceModeResult() - NullPointerException: java.lang.NullPointerException
2019-04-23T21:39:25,439 ERROR qtp1178594393-187 com.vmware.vim25.ws.WSClient java.net.ConnectException: Connection timed out: connect
at java.base/java.net.PlainSocketImpl.connect0(Native Method) - Exception caught while invoking method: RetrieveServiceContent
It found some error message with NotAuthenticated: The session is not authenticated. As i understanding, we need create the local account and assign with correct permission. May i know have any setup document with local account permission assignment can be reference? 
Best Regards
Alan Cheng
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:11 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
0
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:11 AM . Last Modified: ‎2024-03-15 06:02 AM

Hello,

Creating shared local account is discussed on page 62 on the PCNS VMware User's Guide. I have also attached a PDF that discusses the setup. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:11 AM . Last Modified: ‎2024-03-15 06:02 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:11 AM . Last Modified: ‎2024-03-15 06:02 AM

Hello,

Creating shared local account is discussed on page 62 on the PCNS VMware User's Guide. I have also attached a PDF that discusses the setup. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore