Safe to update management card in UPS while its in use?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Safe to update management card in UPS while its in use?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
8
1797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Safe to update management card in UPS while its in use?

Hi All,

I need to update the firmware of our x2 APC Smart UPS 6000 and 1x Smart UPS 3000 management cards which are all AP9619 cards.  The UPS units are all connected to multiple devices and have x2 additional battery packs attached to each one.  My question is can I safely update this firmware 'SFSUMX372' without having any downtime or is the recommended way of doing this to power down devices before its done?  I couldn't find any official documentation on this matter, if someone could send me a link to something official from APC I would be much obliged. 

Thanks for any help!

Rob

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Hi Rob,

Yes, this is safe to do for your scenario. The Network Management Card itself will reboot during the process but this has no affect on the UPS output itself. The same goes for any device that has a Network Management Card and you reboot it or update the firmware.

*There are exceptions to devices such as Rack PDUs/power strips that if they are experiencing communication errors in the event log, they may lose communication with outlet status during a Network Management Card reboot. This is extremely rare but I have seen it before. What I said above applies to a typical scenario where there are no critical errors present on your Network Management Card relating to its own status. The communication alarm I noted would be present as a critical alarm. This behavior does not happen on a UPS though since a Switched Rack PDU is a different animal.* I just wanted to note that here though in case anyone else comes across this post in a search.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Hi All,

I need to update the firmware of our x2 APC Smart UPS 6000 and 1x Smart UPS 3000 management cards which are all AP9619 cards.  The UPS units are all connected to multiple devices and have x2 additional battery packs attached to each one.  My question is can I safely update this firmware 'SFSUMX372' without having any downtime or is the recommended way of doing this to power down devices before its done?  I couldn't find any official documentation on this matter, if someone could send me a link to something official from APC I would be much obliged. 

Thanks for any help!

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Anyone know anything about this?!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Hi Rob,

Yes, this is safe to do for your scenario. The Network Management Card itself will reboot during the process but this has no affect on the UPS output itself. The same goes for any device that has a Network Management Card and you reboot it or update the firmware.

*There are exceptions to devices such as Rack PDUs/power strips that if they are experiencing communication errors in the event log, they may lose communication with outlet status during a Network Management Card reboot. This is extremely rare but I have seen it before. What I said above applies to a typical scenario where there are no critical errors present on your Network Management Card relating to its own status. The communication alarm I noted would be present as a critical alarm. This behavior does not happen on a UPS though since a Switched Rack PDU is a different animal.* I just wanted to note that here though in case anyone else comes across this post in a search.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Wow thanks Angela, that is a very helpful response!

One more question if I may (although I don't mind if you want me to repost as a separate question):

When running the firmware update file in Windows it asks me to put in a username and password.  I put in the username and password that I use to login to the web interface but it returns a login failed message.  Is there a restriction on the length of the password of something in the utility as we do use long passwords here.

Thanks

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

Yes, there is I believe. I noted it in this article now that you reminded me -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US

"If using the NMC1 executable, You will then be prompted to either 1) Continue with upgrade 2) Re-enter Parameters 3) Quit. Choose option 1 then enter. *In NMC1 Upgrade Utility v1.2 or higher, a username or password longer than 11 characters will be truncated. Thus, you will need to change the password to 11 characters or less or choose another firmware upgrade method. Reference the picture below on how to check your NMC Upgrade tool version."

I believe the firmware tool you're using is indeed v1.2 if you look on the top left of the command prompt window it launches.

Let me know if you have any other questions Rob.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

Hi Angela, thank you very much - with your help I was able to get everything up and running.  You really know your stuff and are a credit to your team!

Cheers

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

Angela,

In regards to your comment "The same goes for any device that has a Network Management Card and you reboot it or update the firmware." for future clarity:

I believe the larger UPS units (Symmetra PX, etc) do shut down each module at a time to perform an update IF there is enough spare capacity to do so (N+1). So it doesn't "shut down" the unit but it does cycle the power modules. Also, I am sure you know, the InRows shut down for about a minute when they receive an update.

Regards,

J

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:41 AM . Last Modified: ‎2024-03-05 12:29 AM

Hi J,

I am not aware of that requirement - only on Symmetra PX 250/500kVA where a field service engineer needs to perform the update and typically do a UPS update at the same time. I am not too familiar with the InRows either embarassed so my statement comes from experience with single phase UPS models and most 3 phase UPS models as well as Rack PDUs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.