How can I perform a runtime calibration when the load on the UPS is only 21%?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How can I perform a runtime calibration when the load on the UPS is only 21%?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
4
11482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

How can I perform a runtime calibration when the load on the UPS is only 21%?

I just replaced the battery pack in a rack mount Smart-UPS 3000.

The batteries have charged up to 100% but the runtime only shows 6 minutes.

It's been recommended that I perform a calibration but the guidelines indicate that the load should be at least 30%.

The load on the UPS is at 21%. Can I run the calibration anyway?

2343_UPS.png

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
11483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Another option is a manual calibration, outlined here for something similar -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
11483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

HI, while APC recommends at least 25 % load, I would not be concerned about being low by 5%. This is especially true given your runtime is reporting as way too low; which means the UPS's internal "battery constant" ( a hexadecimal variable that the UPS's cpu constantly updates in its internal flash memory as it goes on and off battery over time) is out of whack....  the lower load will allow the UPS a better chance to do a calibration accurately...in my experience if the battery constant is seriously out of whack and the load on the UPS is high the calibration doesn't always give the expected results:   at 20% load on a 3000 VA ups (and no external batteries) the runtime should be around 40 to 50 minutes.

Try the calibration and if you are still seeing 6 minutes afterwards you will either need to brain dead the UPS to try re-setting the constant ( which means run it on battery under load until the UPS dies and shuts off, then pull the battery, press and hold the on button for a bit to discharge the UPS internally (capacitors), then connect the battery and power up again). Or, you can try to get one of APC's "CalKey" dongles (only works on older smart-ups), or there is a way of changing the constant using hyperterminal to the serial port on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
11483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Another important thing for doing a calibration is making sure the load does not fluctuate a lot. I also suggest giving it a try and let me know if it does not work and we can explore different options.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
11483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Thank you. I will try the calibration as it is and report back with the results.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

0 Likes
0
11484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:40 AM . Last Modified: ‎2024-03-05 12:29 AM

Another option is a manual calibration, outlined here for something similar -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of