SYRMXR4B4 (SYXRCC) Communication Card fault error XX L1 F2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYRMXR4B4 (SYXRCC) Communication Card fault error XX L1 F2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

0 Likes
4
2252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

SYRMXR4B4 (SYXRCC) Communication Card fault error XX L1 F2

Just out of curiousity, does anyone know what an XX L1 F2 error on the SYXRCC is, where XX is the frame number? I purchased a spare card because these are practically the only thing that fails in Symmetras other than the batteries and I always like to have a spare. I swapped this new card with a working card and it displayed "03 08" when booting (this is frame number 3) and then switched to "03 L1 F2", where the F is missing its top segment. All the main frame reports is "Battery Module Fault" I switched back to my good card and everything is back to normal, but before I talk to the seller, does anyone know what this error is?

Also, it would be wonderful if someone posted the complete list of errors and what they really mean. The single errors you find when searching the main site are all "reseat the card and replace if that doesn't fix it" and search is missing most of the error codes. A PM with the info is fine if you don't want to post it for public consumption.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

0 Likes
0
2252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

Thanks. I assume the card drives the front panel LED segments directly, so if the card sends gibberish the display can do odd things. I've had that card in and out a few times, as well as my original card and another spare (both of those work), so I think it is just broken. I had a look at the logic on the card and it looks like there is only one A/D converter which gets switched among the possible battery sense leads. So it isn't a simple case of a bad chip on the card. So I'll send the card back to the seller and ask for a replacement or refund. Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

Hi Terry. These are indicating the location of which batteries the frame sees as bad. In this case L1 battery and the other letter is an r--so the frame is seeing a bad battery at L1 and R2 in the XR frame.   

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

Ok. So whatever senses the battery status on the SYXRCC is bad (since things are fine with the other, known-good card)? I don't remember what the other cards (from a year ago and further back) were reporting as errors. These cards do seem to go bad an order of magnitude more than any other card in the UPS, which explains why so many of the ones on ebay are bad - they're cards that were pulled and replaced because they failed.

Also, the xx 08 at boot time doesn't matter and is something like the firmware version on the card?

Edited to add: I'm pretty sure the top left vertical segment was lit, making this an F without the top bar and not an r. Also, the UPS didn't see any batteries when this chassis was connected to the UPS with the bad card in it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

Hey Terry. There is no F fault code--so I am not sure what we are seeing. That digit can display 0, E, r, c, L. If that card is seeing the batteries as bad and other cards are not then you could try reseating the batteries and running a self-test to see if that clears the issue. When the cards boot up they will show 8.8 and other characters. It is just going through its boot-up process. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:30 AM . Last Modified: ‎2024-03-07 11:01 PM

Thanks. I assume the card drives the front panel LED segments directly, so if the card sends gibberish the display can do odd things. I've had that card in and out a few times, as well as my original card and another spare (both of those work), so I think it is just broken. I had a look at the logic on the card and it looks like there is only one A/D converter which gets switched among the possible battery sense leads. So it isn't a simple case of a bad chip on the card. So I'll send the card back to the seller and ask for a replacement or refund. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore