SURTD3000XLT + AP9626 in United States

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURTD3000XLT + AP9626 in United States
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:44 AM

0 Likes
3
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:44 AM

SURTD3000XLT + AP9626 in United States

Hey! Thank you for checking this out.

I just got my hands on a second-hand SURTD3000XLT. I want to use this in my server rack in my home. 

My electrical panel allows me to use two (120v) rails in order to get 240v (probably 248v since I'm measuring 124v per rail with no load attached). 

I saw that the SURTD3000XLT is usually paired with a Step-Down transformer (specifically the AP9626) so I purchased one separately. 

Before I invest more money in purchasing batteries for the SURTD3000XLT, I'd like to hear from others who might have implemented the same stack in their environment. The NEMA L6-30P plug/receptacle has only 3 prongs (2x hot, 1x ground) - I'm assuming that Neutral is not required for the operation of this UPS. The UPS itself seems to be able to take anything from 180v to 280v.

I'd like to understand whether the output of the SURTD3000XLT will always be 208v (or can be configured to that output no matter the input), because from reading the manual of the AP9626, the input range for it is 185v to 230v. My fear is that since the SURTD3000XLT will be powered from 240v (or 248v), the output of the UPS will be too high for the AP9626.

Please help me understand whether my fear is founded or not.

Thank you very much,

IonutZ

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:44 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:44 AM

Hi John,

The SURTD3000XLT is configurable to 208 VAC or 240 VAC. If it is being supplied to 208 input, then it should be configured to 208 and same if 240:240. You will need to install the PowerChute Business Edition to access it's interface via the Serial connection to change the voltage settings. Or having a Network Management Card.

Even though that it can handle 160 to 280 VAC, it does not mean that it will not react. Once it goes way beyond it nominal voltage of 208/240, it will switch over to battery.

Should you need a 120VAC output, you will need a step-down transformer. But the AP9626 is just applicable for 208 VAC and cannot work with 240VAC. You better off using the SURT003 as this is a Step-Down / Isolation Transformer. You can select if it should work with 208 or 240.

Hope this helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:44 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:44 AM

lonutZ,

The SURTD3000 will work fine for servers in a house.  You are right that input of 208 or 240volt wont matter and L630 is good for upto 250volt  As for output you have 2 options:

1 - Take your 240volt input from your house.  Change the Setting through the Netcard on the UPS to output 208volt and use the simple dumb AP9626 for 120volt loads.  BUT then the bypass wont work as you will be letting 240volt pass through to transformer.  The SURT is NOT a transformer or voltage changer during bypass mode.  The AP9626 will step it down but only to 150volt.

2 - BETTER.  Run your servers and everything at 240volt. Take 240volt power in and output 240volt.  Buy a high voltage PDU (AP7541) and buy PDU C13/C14 server cables to connect your equipment.  Avoid the transformer and legacy 120volt cables. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:44 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:44 AM

I think number 2 is a great suggestion. I looked at my devices and seems that all the critical ones will take 110-240v so that's great 🙂 I thought about this in the beginning but went too far down the rabbit hole with the AP9626 unfortunately, thanks for bringing me back.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:44 AM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:56 PM . Last Modified: ‎2024-03-07 01:44 AM

Hi John,

The SURTD3000XLT is configurable to 208 VAC or 240 VAC. If it is being supplied to 208 input, then it should be configured to 208 and same if 240:240. You will need to install the PowerChute Business Edition to access it's interface via the Serial connection to change the voltage settings. Or having a Network Management Card.

Even though that it can handle 160 to 280 VAC, it does not mean that it will not react. Once it goes way beyond it nominal voltage of 208/240, it will switch over to battery.

Should you need a 120VAC output, you will need a step-down transformer. But the AP9626 is just applicable for 208 VAC and cannot work with 240VAC. You better off using the SURT003 as this is a Step-Down / Isolation Transformer. You can select if it should work with 208 or 240.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore