APC SMART 3000XL - No RUNTIME Information

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SMART 3000XL - No RUNTIME Information
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

0 Likes
2
1616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

APC SMART 3000XL - No RUNTIME Information

Hello,

I have a problem with and UPS SMART 3000XL no showing RUN TIME information. The UPS has three batteries attached (and is showing charge information). The problem began after installing the additional batteries modules (2 additional modules). We try to complete discharge the UPS after installing the battery packs, but we are no getting any RUN TIME information. Could you please give me a suggestion of which process should I follow in order to have the RUN TIME information. Check attached PowerChute UPS status photos.

BR.

RB

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

0 Likes
0
1616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

Hi Rafael - 

It is important to first make sure that you have added the batteries in the Powerchute interface. You would then want to run a manual battery calibration. For this to be effective you will want to make sure that the batteries are 100% charged, at least a 30% load is attached to the UPS, and that the load does not fluctuate more than 5%. From there you can unplug the UPS from input power and allow it to fully drain until it drops the load. If the load is not over 30% or if you turn off the UPS before it drops the load, the runtime data will not be updated. Once the battery is fully drained and drops the load, plug the UPS back in and recharge to 100%. With 2 external batteries this could take up to 24 hours.

thanks,

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

0 Likes
0
1616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

Thats a common problem with RT units.   Remember there is no way for the UPS to really learn about runtime unless it actually does a self test or has a power loss.  Voltage readings are meaningless when the unit is on.

Best thing to do is disconnect the XR cabinets and put just the newest RBC battery trays in the main unit.  Then do a self test.  Once you have a good baseline, you can try adding more cabinets and trays.

For RT units, your runtime is based on your WORST battery as they are all connected.  Have one bad battery, you will have 0 runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

0 Likes
0
1617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:55 PM . Last Modified: ‎2024-03-07 01:45 AM

Hi Rafael - 

It is important to first make sure that you have added the batteries in the Powerchute interface. You would then want to run a manual battery calibration. For this to be effective you will want to make sure that the batteries are 100% charged, at least a 30% load is attached to the UPS, and that the load does not fluctuate more than 5%. From there you can unplug the UPS from input power and allow it to fully drain until it drops the load. If the load is not over 30% or if you turn off the UPS before it drops the load, the runtime data will not be updated. Once the battery is fully drained and drops the load, plug the UPS back in and recharge to 100%. With 2 external batteries this could take up to 24 hours.

thanks,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore