SURT8000XLI: battery inside RBC44 pack

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT8000XLI: battery inside RBC44 pack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
6
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

SURT8000XLI: battery inside RBC44 pack

Hi,
the battery level of my SURT8000XLI drops to 60% during selftest, so I'd guess they are going away.
I know the batteries inside the pack are 12V 5Ah VRLA (8 battery each pack).
Someone can tell me which battery connectors should I choose: batteries contained in the pack (I can't shutdown the UPS for removing and opening the packs) have faston F1 or faston F2 connectors?
Thanks a lot. πŸ™‚

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:42 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:42 AM . Last Modified: β€Ž2024-03-13 01:32 AM

Yes indeed, that was the reason why I want to shut the UPS down. And I fear for battery backup lack in the meantime πŸ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

these batteries are not designed to be field replaceable - it is intended to just purchase the correct number of RBC44 when you are ready to replace your batteries.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000XLI

as shown your UPS would require (2) RBC44. we provide these in modules so you don't need to worry about what you're asking.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

Hi, thanks for the reply.
Since the UPS is not under warranty anymore and in the past I received new original battery packs partially sulfated, I would prefer to buy, test, and change the batteries by myself in this case. Rebuild the battery pack is quite simple.
I apologize if could not write the question here. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

no, its OK. you can ask whatever you like. was just sharing what i know and i understand we also have customers that do what you do as well. and its not under warranty, so you can surely do whatever you'd like. i just know that we cant provide any of that information out directly.

it isnt possible to just swap out the batteries in the module itself?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

If I understand correctly what you mean in the last phrase (I'm not native english), yes, but I have to put offline the UPS to extract packs and then choose and buy batteries with the right connector.
If I would succeed in getting the connector information, I will shutdown the unit only for battery swapping.
Thanks anyway πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:41 AM . Last Modified: β€Ž2024-03-13 01:32 AM

the batteries in the UPS should be hot swappable - meaning you could swap them while the UPS is online. you'd have no battery back up at that time though - is that why you want to shut the UPS down?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:42 AM . Last Modified: β€Ž2024-03-13 01:32 AM

0 Likes
0
1127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:42 AM . Last Modified: β€Ž2024-03-13 01:32 AM

Yes indeed, that was the reason why I want to shut the UPS down. And I fear for battery backup lack in the meantime πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore