Posted: 2021-06-30 08:14 PM
This question was originally posted by AHMED on APC forums on 1/19/2017
I have a fault in an APC SURT10000XLI ups
The red led of the fault is on
the green Led's to the right show as the following:
0
1
0
0
0
Please advise how to fix
Posted: 2021-06-30 08:14 PM
This reply was originally posted by AHMED on APC forums on 1/21/2017
Many Thanks for great info.
I will try it and get back
Posted: 2021-06-30 08:14 PM
This reply was originally posted by Merick on APC forums on 1/20/2017
Hi Ahmed,
Based on the info you gave us the fault you're getting is a "DC Bus Over Voltage", I would recommend that you "Braindead" the UPS and see if it will recover from the fault condition, if it doesn't do call our Technical Support at 1-800-800-4272 and provide the model and serial number of your unit to know your options in replacing the unit.
Below is the link on how to braindead the UPS :
Regards
Posted: 2021-06-30 08:14 PM
This reply was originally posted by AHMED on APC forums on 1/21/2017
Many Thanks for great info.
I will try it and get back