I have a fault in an APC SURT10000XLI ups
The red led of the fault is on
the green Led's to the right show as the following:
0
1
0
0
0
Please advise how to fix
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 2024-03-07 12:31 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 2024-03-07 12:31 AM
Hi Ahmed,
Based on the info you gave us the fault you're getting is a "DC Bus Over Voltage", I would recommend that you "Braindead" the UPS and see if it will recover from the fault condition, if it doesn't do call our Technical Support at 1-800-800-4272 and provide the model and serial number of your unit to know your options in replacing the unit.
Below is the link on how to braindead the UPS :
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 2024-03-07 12:31 AM
Many Thanks for great info.