We are relocating our servers. We have 3 APC SUA2200RM2u (120V).
What power outlet and rating do we need for these?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 3 weeks ago
Hi,
The SUA2200RM2U requires 20 amp 120 volt input. The plug type is NEMA 5-20. Here is a link to the data sheet http://datasheet.octopart.com/SUA2200RM2U-APC-datasheet-11971591.pdf