Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 08:11 AM . Last Modified: 2024-03-12 03:14 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:11 AM . Last Modified: 2024-03-12 03:14 AM
Hi!
I bought one SURT10000XLI. I need 220V to the output. At the building, I have 110V. I can use 2 phase (110V+110V) to power ON the UPS? The manual doesn't show anything about it.
Thank you!
Marcelo
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:11 AM . Last Modified: 2024-03-12 03:14 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:11 AM . Last Modified: 2024-03-12 03:14 AM
Hello,
I checked with our EMEA support team.
Technically it does work.
One problem is however that the breakers of the XLI SKUs are only single-pole breakers which is fine in a P-N system where it is not necessary to break N but in a P-P system it always leaves one hot phase unbroken. So we do specify/recommend to use external dual-pole breakers...
Another point to look at would be proper grounding which is often neglected in P-P systems.
So overall using SURT XLIs in a P-P system is possible if the right safety measures are in place but we do not actively promote this type of applications exactly because of those possible safety issues.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:11 AM . Last Modified: 2024-03-12 03:14 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:11 AM . Last Modified: 2024-03-12 03:14 AM
Thank you.