Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Redundant UPS - single UPS Failure - some servers shutdown, others do not

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Redundant UPS - single UPS Failure - some servers shutdown, others do not
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:10 AM . Last Modified: ‎2024-03-12 03:15 AM

0 Likes
5
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 AM . Last Modified: ‎2024-03-12 03:15 AM

Redundant UPS - single UPS Failure - some servers shutdown, others do not

Hi,

Wie have 2 SURT 10.000 XL behind 3 Bladecenters.

Using PCNS in redundant configuration

Shutdown only if UPS is on battery after 120s

Recently the batteries from 2006 failed in one of the two UPS - most Systems ignored that as expected because the other UPS still was alive.

But: 3 Servers (w2k8, W2k12) in one of the Bladecenters went into a Boot-circel:

I switched them on, OS is starting, PCNS shuts down the system.

These steps did not help:

- removing the IPs from the UPS-GUI, everytime the server came up and alive the IP showes up in the UPS GUI again and the server shuts down.

- setting the USV into Bypass-Mode

I had to remove eth-cable from the UPS and stop PCNS-Service on these three machines. I can see on the client-side, that both UPS are connected and configured.

Is there any idea what to do to prevent such behavior?

Thnx - Chris

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:14 AM

Hi,

The logic is, if 1 of the 2 UPS cannot support the entire load by itself then it is deemed not safe and since you have selected shutdown for runtime exceeded action should be taken. The solution is to correct the issue as described in the help file. You can also configure the UPS to not provide power until the batteries have charged properly and that will prevent the looping.

In your case since the UPS may or may not charge properly so the runtime will always be low I would stop the PCNS service, edit pcnsconfig.ini on the affected systems and deselect shutdown due to runtime is exceeded (event_RunTimeExceeded_enableShutdown = false)  until the batteries are replaced.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:10 AM . Last Modified: ‎2024-03-12 03:15 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 AM . Last Modified: ‎2024-03-12 03:15 AM

Chris,

What version of PCNS is installed and what is logged in EventLog.txt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:15 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:15 AM

Hi Bill,

PCNS 3.01 build 2650

Eventlog-snap:

04/14/201416:41:05PowerChute successfully opened UDP port 3052..3.4.9.9
04/14/201416:41:06PowerChute Network Shutdown version 3.0.1 started.3.5.1.5.6.10
04/14/201416:41:06PowerChute successfully opened TCP port 3052..3.4.9.9
04/14/201416:41:06PowerChute successfully opened TCP port 6547..3.4.9.9
04/14/201416:41:08Network Management Card apc4.xxx.com communication has been established..3.5.1.5.6.13
04/14/201416:41:08Communication established with Environmental Monitoring Card.3.5.1.7.20
04/14/201416:41:08Network Management Card apc5.xxx.com communication has been established..3.5.1.5.6.13
04/14/201416:41:08Communications have been established..3.5.1.5.6.1
04/14/201416:41:08Communication established with Environmental Monitoring Card.3.5.1.7.20
04/14/201416:41:08Available runtime has been exceeded..3.5.1.6.1
04/14/201416:41:25Shutdown process started. Windows will shut down soon..3.5.1.4.3

It is indeed configured to shutdown when runtime is exceeded - but runtime is only on "apc5.xxx.com" exceeded - "apc4xxx.com" is not affected.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:15 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:15 AM

Hi,

If one of the 2 NMCs report runtime has been exceeded PCNS will start OS shutdown.

This is from the PCNS help file

Available runtime has been exceeded:

This event is always logged and, on a Redundant-UPS configuration, event actions are carried out even if it occurs on only one Network Management Card.


To correct the issue you will need to resolve the reported issue.

Two configuration conditions can cause this event:

  When the command file time on the Configure Shutdown page plus 10 seconds is greater than the Low Battery Duration field value. (A low battery condition always causes a shutdown, so when it occurs the UPS must have enough time available to complete shutdown activities). To fix this, either decrease the command file time, or increase the Low Battery Duration value. (To change the Low Battery Duration, on the Network Management Card user interface select the UPS tab and Configuration - shutdown).

  When the UPS runtime is less than the sum of the shutdown delay time configured for the UPS: On Battery event plus the command file time on the Configure Shutdown page, minus two minutes. This condition can be caused by having too much load on the UPS, or by the UPS batteries not being fully charged. If the UPS batteries are fully charged, to fix this a) remove some equipment from the UPS, or b) decrease the shutdown delay time for the UPS: On Battery event, or c) decrease the command file execution time on the Configure Shutdown page.



Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:14 AM

Thank you Bill.

Although it seems as "works as designed" this "design" makes not any sense to me:

If I configure a "redundant UPS setting" I exactly expect that it is redundant in any way - but if a shutdown is always initiated when a "runtime exceeded" failure is noticed on ONE of my "nodes" the whole configuration is not to be called "redundant" - if in an clustered server enviroment any node logs a failure and the whole cluster would shut down nobody would need to setup a cluster.

And: What is the correct solution to avoid that shutdown-circle? I thought to put the failed UPS in Bypass-mode or to remove the Server-IP from the UPS, but both of these things did nod help and I cannot imagine that I always have to plug of the NMC or the cable to stop all the servers to shutdown permanently until new RBCs arrive.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
1096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 AM . Last Modified: ‎2024-03-12 03:14 AM

Hi,

The logic is, if 1 of the 2 UPS cannot support the entire load by itself then it is deemed not safe and since you have selected shutdown for runtime exceeded action should be taken. The solution is to correct the issue as described in the help file. You can also configure the UPS to not provide power until the batteries have charged properly and that will prevent the looping.

In your case since the UPS may or may not charge properly so the runtime will always be low I would stop the PCNS service, edit pcnsconfig.ini on the affected systems and deselect shutdown due to runtime is exceeded (event_RunTimeExceeded_enableShutdown = false)  until the batteries are replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore