SURT 6000Kva + Step Down transformer to Transfer Switch - Different voltages?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT 6000Kva + Step Down transformer to Transfer Switch - Different voltages?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
1
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

SURT 6000Kva + Step Down transformer to Transfer Switch - Different voltages?

I have a pair of SURT 6Kva UPS units, each with the same model and type od APC step down transformer.
I use an APC ATS (Auto Transfer Switch) across each transformer to provide redundant power to my 110v devices with a single power cord.

In the measurement section of the ATS, I see that the input voltages on each side wander around slightly, but always are about 5 volts off from each other.
Here is what I see:

Source Measurements
  Source A Source B
Input Frequency:  60 Hz  60 Hz
Input Voltage:  124 VAC  121 VAC

So, I looked in the UPS  status pages on each UPS and I see less than 1v deviation between the output voltages of each.
Like so...

UPS-A

Power
Input Voltage: 243.3 VAC
Output Voltage: 209.4 VAC
Input Frequency: 60.02 Hz

UPS-B

Power
Input Voltage: 244.8 VAC
Output Voltage: 208.2 VAC
Input Frequency: 60.02 Hz

Why would the voltage be so different at the ATS measurements page?
Can I adjust this or "tune" it via some interface or by making some internal adjustment?

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

Hi Lenny - 

I see that your ATS is 120v and your UPS is inputting nominal 240v and outputting nominal 208v. Ideally in this situation you would be outputting 240v and use a 240v to 120v stepdown (I didnt see the model of your transformer listed so I'm not sure if you have a model that could do this or not.)

A 240v to 120v stepdown outputs 50% of the input. So if you feed it 240v, it outputs 120v. If you fed it 246v it would output 123v.

A 208v to 120v stepdown outputs roughly 0.577 of the input. If you feed it 208v, it outputs 120v. If you feed it 212v, it outputs 122v

The output of your SURT is typically within 3% of what it is set for, which in your case is 208v. This is going to fluctuate some, and the output of your transformer will always be a set % of the UPS output. The ATS uses a different chipset to measure voltage than the UPS does, and there is always a slight lag between measurement and reporting. You may find that they are not always 100% in agreement, but they will be close.the output is always going to be well within CBEMA standards for voltage regulation in IT environments. From your numbers it appears that the calibration on the ATS reporting may be off slightly. You could double check it with a quality voltmeter if it is critical to your application. 

 

Hope this helps,

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

Hi Lenny - 

I see that your ATS is 120v and your UPS is inputting nominal 240v and outputting nominal 208v. Ideally in this situation you would be outputting 240v and use a 240v to 120v stepdown (I didnt see the model of your transformer listed so I'm not sure if you have a model that could do this or not.)

A 240v to 120v stepdown outputs 50% of the input. So if you feed it 240v, it outputs 120v. If you fed it 246v it would output 123v.

A 208v to 120v stepdown outputs roughly 0.577 of the input. If you feed it 208v, it outputs 120v. If you feed it 212v, it outputs 122v

The output of your SURT is typically within 3% of what it is set for, which in your case is 208v. This is going to fluctuate some, and the output of your transformer will always be a set % of the UPS output. The ATS uses a different chipset to measure voltage than the UPS does, and there is always a slight lag between measurement and reporting. You may find that they are not always 100% in agreement, but they will be close.the output is always going to be well within CBEMA standards for voltage regulation in IT environments. From your numbers it appears that the calibration on the ATS reporting may be off slightly. You could double check it with a quality voltmeter if it is critical to your application. 

 

Hope this helps,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore