SMX750 & AP9631 Not Talking after Firmware update(s)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX750 & AP9631 Not Talking after Firmware update(s)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
4
1231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

SMX750 & AP9631 Not Talking after Firmware update(s)

I have an SMX750 with AP9631 installed.  I was having a lot of alerts/transfers due to "distorted input".  I read on this forum that a firmware upgrade may help.  I updated the Firmware on the UPS from 9.9 to 10.1 using Firmware Upgrade Wizard v4.1.1 per instructions.  After the upgrade the AP9631 could not see the UPS "No UPS Found".  Re-reading the instructions, it appears that they recommend removing the card during firmware update, which I did not do (I only disconnected the network).  The upgrade succeeded per the tool and all appears normal on the UPS other than no network information in the 'About' section (UPS can't see network card either)

Troubleshooting I already tried:

  1. Rebooted Network Management card
  2. Fully power cycled unit (disconnected battery and unplugged)
  3. Re-seated Network card
  4. Tried removing card and re-sending firmware, but firmware upgrade wizard could not find it (not sure if this is due to it already being upgraded)
  5. Upgraded NMC firmware from 6.5.0 to 6.8.8 (I was a little worried about this as 10.1 firmware notes include compatibility with NMC 6.5.0)
  6. Contacted support and they wanted next step for me to connect directly to the NMC with putty to do? (had to stop working on it at this point)
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9631
  • firmware
  • smx750
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

Thanks for the reply.

I worked for a couple of hours with APC support and we were not able to fix the issue.  They sent me a replacement that came with 9.8 firmware and directed me not to try and upgrade it:)

I went to see what I am missing between 9.8 and 9.9 and it looks like they pulled the latest firmware from their website for SMX series.  I am guessing I am not the only one that had an issue with the 10.1 upgrade.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

Update:

-I tried a new 9631 card and still same issue

-I also tried connecting a laptop with PowerChute Business Edition and it finds the UPS during install on USB, but the software cannot see UPS status when I log in after install

I wish I could just downgrade the firmware on the UPS back to 9.9 grrrr.

I talked to Tech support and the 4.1.1 firmware upgrade wizard won't even re-send the firmware if it sees a device with the latest firmware....

Reply

Link copied. Please paste this link to share this article on your social media post.

sdas_apc
Crewman sdas_apc
Crewman

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

I have a SMT1000 with AP9630 in it and faced a similar sort of issue after the NMC firmware upgrade. then figure-out I have flushed with a wrong firmware. When I upgraded with this: P-SFSY688 I got the similar 'No UPS found'. Then re-flushed with P-SFSUMX688 and things came back again. Probably something similar happened?

IMO, firmware upgrade should check the compatibility before blindly applying/upgrading the firmware. That wasn't expected from APC!!

-S 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:23 AM . Last Modified: ‎2024-03-15 05:41 AM

I have also upgrade to 10.1 and no connection, no USB no serial. Only modbus over serial when I activate on LCD.

Here is the old working firmware 9.8:

https://www.apc.com/au/en/faqs/FA281865/

> All images with Read Me Files

The downgrade is only over serial cable possible. Disconnect battery and all cables, also main. Connect the serial cable, press and hold the buttons "on/off" and "down" and connect the main cable, hold the buttons up the Error LED is blinking.

Now you have a short time to start the firmware upgrade wizard...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:24 AM . Last Modified: ‎2024-03-15 05:41 AM

Thanks for the reply.

I worked for a couple of hours with APC support and we were not able to fix the issue.  They sent me a replacement that came with 9.8 firmware and directed me not to try and upgrade it:)

I went to see what I am missing between 9.8 and 9.9 and it looks like they pulled the latest firmware from their website for SMX series.  I am guessing I am not the only one that had an issue with the 10.1 upgrade.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore