SUA750XL with new batteries: ran then lost calibration - what to do next?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA750XL with new batteries: ran then lost calibration - what to do next?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
6
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

SUA750XL with new batteries: ran then lost calibration - what to do next?

I recently replaced the batteries on my SUA750XL. It charged up to 100% but had the "blinking charge level" indication, and showed estimated runtime = 0, which I know mean I needed to do a runtime calibration. I let it charge overnight.

Since I am using Linux (trying both nut and apcupsd) and use a USB cable, I couldn't find a way to run a soft calibration. (If there is a way, I would like to know it). So I did a "hard" calibration, by removing the server, connecting 250W of light bulbs (=40% load), pulling out the power, and letting it run to exhaustion - which took about 50 minutes. Then I plugged in to mains with no load and let it charge up to about 50% or so, and then added my server (which is about a 20% load). At that point it was still charging but showed a reasonable expected run time (I think it was well over an hour). So far so good.

Unfortunately I did something I was about to regret: I started a self-test (from the panel). The charge level which had been around 50% dropped to 0 instantly, the estimated runtime returned to zero, and the server shut down. When I brought the server back up, I found that it still showed 0 runtime (and was blinking again!) - i.e. it lost the calibration. It charged back to 100% but alas still was blinky.

I disabled the server software and pulled the mains. As expected, it powered the load just fine for several minutes, i.e. it had plenty of battery capacity. I plugged it in again, and now it shows 3 minutes runtime - about the amount of time I had unplugged it.

So finally, my questions:

- while it was recharging, was the calibration still considered "in progress"? and did hitting the self-test cancel it? do I just need to do it again and not screw it up this time? (i.e. let it charge all the way to 100%)? or does it sound as if something else is wrong?

- if I do need to rerun the calibration, how much damage am I doing to my brand-new batteries to cycle them twice in a couple days? if it's bad, is there any reasonable alternative?

I guess what I'm worried about is that I will re-run the calibration, then lose it again at the next self-test, because I am doing something wrong.

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

I recently replaced the batteries on my SUA750XL. It charged up to 100% but had the "blinking charge level" indication, and showed estimated runtime = 0, which I know mean I needed to do a runtime calibration. I let it charge overnight.

Since I am using Linux (trying both nut and apcupsd) and use a USB cable, I couldn't find a way to run a soft calibration. (If there is a way, I would like to know it). So I did a "hard" calibration, by removing the server, connecting 250W of light bulbs (=40% load), pulling out the power, and letting it run to exhaustion - which took about 50 minutes. Then I plugged in to mains with no load and let it charge up to about 50% or so, and then added my server (which is about a 20% load). At that point it was still charging but showed a reasonable expected run time (I think it was well over an hour). So far so good.

Unfortunately I did something I was about to regret: I started a self-test (from the panel). The charge level which had been around 50% dropped to 0 instantly, the estimated runtime returned to zero, and the server shut down. When I brought the server back up, I found that it still showed 0 runtime (and was blinking again!) - i.e. it lost the calibration. It charged back to 100% but alas still was blinky.

I disabled the server software and pulled the mains. As expected, it powered the load just fine for several minutes, i.e. it had plenty of battery capacity. I plugged it in again, and now it shows 3 minutes runtime - about the amount of time I had unplugged it.

So finally, my questions:

- while it was recharging, was the calibration still considered "in progress"? and did hitting the self-test cancel it? do I just need to do it again and not screw it up this time? (i.e. let it charge all the way to 100%)? or does it sound as if something else is wrong?

- if I do need to rerun the calibration, how much damage am I doing to my brand-new batteries to cycle them twice in a couple days? if it's bad, is there any reasonable alternative?

I guess what I'm worried about is that I will re-run the calibration, then lose it again at the next self-test, because I am doing something wrong.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

Did you try running another self-test after it reached 100% capacity? I honestly haven't seen what you've experienced before as it's always recommended to run a test at full capacity (though you already seem to know that now!), so odd behavior isn't surprising, though I can't really explain this one, either. Running a self-test should not clear the results of the last complete calibration, though like I've said, I've always waited until after it reached 100%. Maybe attempting that test made it incomplete.

You might need to run another calibration, but honestly, if you know you're actually getting plenty of runtime, you could probably just leave it as it is rather than run another. Like you said, that'll definitely put some decent wear and tear on the batteries, and who knows, it might fix itself when the next power outage or self-test comes along...

Also, that bar graph is only flashing because you're within 2 minutes of the low battery duration. By default, the low battery warning is at 2 minutes, so it thinks you have less than 4 minutes of runtime. If pulling the plug for a couple of minutes upped the runtime to that duration, pull it for 5 minutes (low battery warning + 2m) to at least make it stop flashing.

I'd try that self-test, assuming you haven't already, and see if it makes a difference.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

Hi Larry,

Do you have the Serial Cable that came with the UPS? If so, I would recommend you to call in the APC Customer Care Center in order to verify the Battery Constant value of the UPS, and adjust the battery constant in case if it needs to be changed. I hope that it will take care of everything.

Have a nice day!

:)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

Battery charging is complete when power consumption plateaus out. Not when it indicates 100% charge, so charge 24 hours, then...


Sometimes, APC UPSs don't like seeing voltage between ground and neutral. From my experience, it works better to cause an outage by interrupting just the hot, which can be accomplished by using a power strip with a switch. Let it fully charge, load the UPS to about half the load, then turn the switch off on the power strip. The neutral and ground remains fully connected to the building electrical system.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

I am with Techie on this one. If you know the batteries are good, they hold charge, you just need to adjust the constant. If you don't know the constant off hand, give APC a call and they should reveal it to you. If they don't, post it in this forum and someone will. Changing the constant will adjust the run time to spec.


If you don't have the serial cable, you might just have to go with another calibration. Sometimes they're stubborn and require several calibrations to make it stick.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

Charge overnight, then discharge until it shuts off
Charge overnight and if then, run self-calibration

If that doesn't work adjust the constant over serial port in PROG. Ask APC for the specific value to use

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:34 PM . Last Modified: ‎2024-03-14 01:29 AM

I recently replaced the batteries on my SUA750XL. It charged up to 100% but had the "blinking charge level" indication, and showed estimated runtime = 0, which I know mean I needed to do a runtime calibration. I let it charge overnight.

Since I am using Linux (trying both nut and apcupsd) and use a USB cable, I couldn't find a way to run a soft calibration. (If there is a way, I would like to know it). So I did a "hard" calibration, by removing the server, connecting 250W of light bulbs (=40% load), pulling out the power, and letting it run to exhaustion - which took about 50 minutes. Then I plugged in to mains with no load and let it charge up to about 50% or so, and then added my server (which is about a 20% load). At that point it was still charging but showed a reasonable expected run time (I think it was well over an hour). So far so good.

Unfortunately I did something I was about to regret: I started a self-test (from the panel). The charge level which had been around 50% dropped to 0 instantly, the estimated runtime returned to zero, and the server shut down. When I brought the server back up, I found that it still showed 0 runtime (and was blinking again!) - i.e. it lost the calibration. It charged back to 100% but alas still was blinky.

I disabled the server software and pulled the mains. As expected, it powered the load just fine for several minutes, i.e. it had plenty of battery capacity. I plugged it in again, and now it shows 3 minutes runtime - about the amount of time I had unplugged it.

So finally, my questions:

- while it was recharging, was the calibration still considered "in progress"? and did hitting the self-test cancel it? do I just need to do it again and not screw it up this time? (i.e. let it charge all the way to 100%)? or does it sound as if something else is wrong?

- if I do need to rerun the calibration, how much damage am I doing to my brand-new batteries to cycle them twice in a couple days? if it's bad, is there any reasonable alternative?

I guess what I'm worried about is that I will re-run the calibration, then lose it again at the next self-test, because I am doing something wrong.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of