SUA750I - SMT750I - OID to get output power (Watts)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA750I - SMT750I - OID to get output power (Watts)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
6
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

SUA750I - SMT750I - OID to get output power (Watts)

Hi everyone,
I have SMT-750I and SUA-750I with AP 9630 Network Management Card 2 (FW 6.5) and I need to get the output load power (in watts). I've been trying to do this with an snmpget of 1.3.6.1.4.1.318.1.1.1.4.2.8 OID and I obtained the following results:
SUA 750I - "There is no such variable name in this MIB" 
SMT 750I - = INTEGER : 0
I can correctly get the VA value with snmpget of 1.3.6.1.4.1.318.1.1.1.4.2.3.0 but not the 
Watts value.
When I establish a telnet session with both models of UPS and execute "detstatus -om" I can see that the UPS reports correctly the values of: "Output Watts Percent" and "Output VA Percent".
I want to know if there is any form to get the output load power (in watts) with an snmpget. 
Thanks
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Hi voidstar,

I agree. I found some cases in which the % W it's grater than the % VA, for example the following case:

rJwFsgZaKkDsJR0teXmIIw%3D%3D.jpegrJwFsgZaKkDsJR0teXmIIw%3D%3D.jpeg

I suppose the reason why is that in the case of W% the nominal value is 500 W so power: 0,286 x 500 W = 143 W and in the case of VA% the apparent power is: 0,266 x 750 VA = 199,5 VA. Am I right ?

Bellow you'll find an example of the method results applied to a test set of 45 UPSes (Green : Runtime offset fixed with calibration,  Yellow : Reduced runtime, Red : Very reduced runtime). Cases in yellow or red need needs further analysis to determine the need of battery replacement or other actions. 

Thanks a lot for the information provided.

o3jF8T16gSUgEAzLa8UQrA%3D%3D.jpego3jF8T16gSUgEAzLa8UQrA%3D%3D.jpeg

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Hi,

The OID is 1.3.6.1.4.1.318.1.1.1.4.2.8.0

Description: The total output active power of the UPS system in Watts

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Hi,

I didn't put the final .0 in the last post but I'm using the OID you said.  Bellow you'll find the results obtained with detstatus -om and with the snmpget. As you can see the result of the OID 318.1.1.4.2.8.0 is INTEGER: 0 instead of the 27 that 

shows detstatus -om.

BL6F0J35r9zDHQumcVoNlQ%3D%3D.jpegBL6F0J35r9zDHQumcVoNlQ%3D%3D.jpeg

kVg8um02bh0f0po6%2Fe2S5A%3D%3D.jpegkVg8um02bh0f0po6%2Fe2S5A%3D%3D.jpeg

I hope you can find the solution. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Hi Alvaro,

Make sure you have the latest SUMX (6.5) on the SMT750I UPS... I think there was an issue with 0 being returned before SUMX 6.4. You mentioned having 6.5 there so it should be fine but it's worth checking.

If it is running the latest version, please attach a debug tarball from About->Support->Generate Logs.

Also worth noting: 318.1.1.1.4.2.3.0 is the highest of the w% and va% readings (ie, max(w%, va%)). So it represents load measurement with the least margin whether that's VA or W.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Hi,
thanks for the information, it was useful to me. Considering what you said about the version of SUMX I tested different combinations of UPS model and FW version with the following results.
QlOThmRQLq7WaTm9KZ%2FcFQ%3D%3D.jpegQlOThmRQLq7WaTm9KZ%2FcFQ%3D%3D.jpeg
Considering the results and the models involved, Is it correct to conclude that OID 318.1.1.1.4.2.8.0 it's available only for SMT 750I with FW below 6.4 ?
In your opinion, is there any form to obtain the output power (W) in both models by snmpget ?
The reason why I need the W value is because I'm designing an automatized method to compare the runtime reported by the UPS with the theorical runtime provided by APC in the Runtime Graph http://www.apc.com/products/runtimegraph/runtime_graph.cfm?base_sku=SMT750I&chartSize=large
and conclude if the UPS requires or not a calibration.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Hi Alvaro,

That's a cool table!

I don't think SNMP provides a way to get the wattage on the older SUA units. However, most equipment these days has a power factor of 1 which means Watts = VA. The UPS' max watt rating is always lower than the VA rating. Therefore unless you're powering something really unusual, you can assume 318.1.1.1.4.2.3.0 is % watts.

I'm not clear on the benefits of your automatized method, but maybe I don't have the full picture. The runtime estimate reported should decrease as the battery ages -- the published theoretical runtime graph is for a brand new battery. My understanding is that the UPS' runtime estimate may require calibration when:

 1) The battery is replaced with a new battery rendering the old estimate meaningless

 2) The existing battery's actual runtime decreases but the estimate isn't updated because the UPS hasn't transferred to battery or doesn't have enough load to update the estimate.

For the first case when replacing a battery, the newer SMT/SMX UPSes use the LCD display to ask if the battery has been replaced and update the estimate if so. The older SUA units do not and may require a runtime calibration instead.

For the second case I'm not sure how you would detect that the health of the battery has decreased if the UPS itself hasn't detected it.

You might also be interested in Peukert's law which describes how lead-acid battery capacity varies with load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Hi voidstar,

I agree. I found some cases in which the % W it's grater than the % VA, for example the following case:

rJwFsgZaKkDsJR0teXmIIw%3D%3D.jpegrJwFsgZaKkDsJR0teXmIIw%3D%3D.jpeg

I suppose the reason why is that in the case of W% the nominal value is 500 W so power: 0,286 x 500 W = 143 W and in the case of VA% the apparent power is: 0,266 x 750 VA = 199,5 VA. Am I right ?

Bellow you'll find an example of the method results applied to a test set of 45 UPSes (Green : Runtime offset fixed with calibration,  Yellow : Reduced runtime, Red : Very reduced runtime). Cases in yellow or red need needs further analysis to determine the need of battery replacement or other actions. 

Thanks a lot for the information provided.

o3jF8T16gSUgEAzLa8UQrA%3D%3D.jpego3jF8T16gSUgEAzLa8UQrA%3D%3D.jpeg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of