3 AP7723 Issues I would like help on.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 3 AP7723 Issues I would like help on.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
12
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:14 AM

3 AP7723 Issues I would like help on.

I have been given the task of managing our Rack mounted ATS and PDU at my datacenter. For the last 3 years they just plugged them in and did no form of configuring. Well now I come in and configure them so they can actually work (before all of them had alarms thus could not switch). Upon configuring I have come across 3 issues. none are causing downtime but has stopped the ability to switch over. The issues are:

1- One of the ATS are alerting that the input voltages on both sources have went down to 110 volts in comparison to the 208 they should be. I also noticed that the -12v power supplies in the measuring tool within the ATS shows it at -22
.

2- Another is showing that its frequency is constantly changing from the normal 60hz all the way to 120 Hz and anywhere in between. This is only for source A

3  -Everything is showing out of phase.

Things that you should know are that I have taken a multimeter and tested everything that it could. All firmware is up to date. I am not allowed to unplug anything due to everything being in production. The topology of our power situation is as follows. Each Rack has 2 legs of power fed to it. Lets call them Leg A and B. each ATS has 1 source from each leg of power. those legs are rackmount PDU's that connect to a much larger leibert PDU that is ran off a leibert UPS. We have 2 independent UPS. Any help would be appreciative.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Yes, it will according to What does the "Reset ATS Controller" command accomplish on a Next Gen Rack Automatic Transfer Switch... - for 330-340ms it will cut the output unfortunately. I imagine most equipment will have a problem with that.

In Ohio, we don't have any APC/IT Business Unit facilities so it must be one of the other Schneider Electric BU's facilities. I am in Rhode Island and our facility that does most of the design and evaluation stuff on returned ATS units is in St. Louis, MO.

The one serial number I see for I believe the unit with the frequency issue is mid-late 2012 manufacture date and these have a two year warranty.

I think when you get some time as to not put a risk to the load, we should try to reset the ATS controller and if that does not work, ideally we could replace it for you and take a look at it because I am pretty sure it will still be in warranty at least until the end of 2014. Now on that other one that magically fixed itself when the electrician worked on the other source's UPS, I am honestly clueless unless there is a mistake on what is connected to what and he really did touch the UPS that is feeding that input.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:14 AM

I have been given the task of managing our Rack mounted ATS and PDU at my datacenter. For the last 3 years they just plugged them in and did no form of configuring. Well now I come in and configure them so they can actually work (before all of them had alarms thus could not switch). Upon configuring I have come across 3 issues. none are causing downtime but has stopped the ability to switch over. The issues are:

1- One of the ATS are alerting that the input voltages on both sources have went down to 110 volts in comparison to the 208 they should be. I also noticed that the -12v power supplies in the measuring tool within the ATS shows it at -22
.

2- Another is showing that its frequency is constantly changing from the normal 60hz all the way to 120 Hz and anywhere in between. This is only for source A

3  -Everything is showing out of phase.

Things that you should know are that I have taken a multimeter and tested everything that it could. All firmware is up to date. I am not allowed to unplug anything due to everything being in production. The topology of our power situation is as follows. Each Rack has 2 legs of power fed to it. Lets call them Leg A and B. each ATS has 1 source from each leg of power. those legs are rackmount PDU's that connect to a much larger leibert PDU that is ran off a leibert UPS. We have 2 independent UPS. Any help would be appreciative.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:14 AM

Hello,

Can you clarify - are items #1 and #2 happening on the same ATS?

Too, can you verify the firmware version, just to be sure? Have to ask embarassed - people say it's the latest all the time and sometimes its not so forgive me smile

  • Anyway, on item #1, the -12V power supply is used for voltage and current measurement. So, considering this power supply is faulting, it makes sense to see the weird voltage reading. If under warranty or not, the device should be replaced.

  • Item #2 - Is this the same unit as item #1 - you say "another" so I am thinking no but I wanted to be sure. I'd want to see the logs on this unit if possible and verify whether or not there is an active power supply fault here too. (Instructions on obtaining event.txt, data.txt, and config.ini are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

  • Item #3 - It is rare that two input power sources are in phase completely (meaning 0º phase angle). Our Rack ATSs can support out of phase switching up to 180º degrees, depending on firmware, so this is likely a non issue unless the firmware is really out of date (more technical info here -> http://www.apcmedia.com/salestools/THON-7GTPY6/THON-7GTPY6_R5_EN.pdf). Ideally, those two legs of power you mentioned are from each one of the independent UPSs you mentioned...?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

2267_freq.jpg2268_firmware.jpg

Yes these are 2 different ATS but same model. the above is the one with frequency issues and the below is the one with voltage issues. Both with same version.(its the version the apc guy told me was most recent.). All my ATS and PDU that are rackmounted shows out of sync. I attached the logs from about 2 days ago but this issue honestly probably been happening for months or years before i came along. The most awesomely drawn pic is the power arrangement. so hopefully it explains things more.

2269_volt.jpg2270_phase.jpg

Attachments
data.txt.zip
event.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Ok, thank you. And the picture was nice wink

yes, the firmware is the latest.

On the first one, I am surprised there is no other fault here (power supply, etc) along with this problem. Ultimately though, this should be replaced. If you can, the only thing you could try would be to reset the ATS controller under the Unit->Controller menu but if you do, please read this first -> What does the "Reset ATS Controller" command accomplish on a Next Gen Rack Automatic Transfer Switch... because depending on the attached load, it could reboot/turn off briefly. It could reset the reading though, especially since there is no other fault.

On the second one, it seems like this is all related to the power supply fault. Does the unit actively report a power supply fault within the 5 active alarms it has? (or can you give me the event.txt for that one?)

And for the out of sync stuff, this is normal. It is not likely the two sources will be in sync because they are least several degrees apart. But, you won't see this as an alarm like I said because the ATS can switch sources if they are out of source.

So, it is likely these two units need to be replaced because of the frequency and voltage readings if the resetting of the ATS controller does not help the first one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Without the customers approval I cant unplug anything or do anything that would result in power loss. given the frequency one has nothing plugged in it and the voltage has only 1 thing but still. Also here are the event logs.

Attachments
eventvolt.txt.zip
eventfreq.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Update. Soooo.... This last Saturday we had our electricians replace our UPS batteries as per another issue. I checked the ATS logs for the one with frequency issues and it cleared about 5 minutes of when the electricians finished. So that appeared to be an UPS issue. The weird thing is how Source A has the issue the UPS that was worked on was source B. So they shouldnt be connected but are. I checked the one with the voltage issue and it is still alerting the same as before. However when I telneted to it it said that the power supply that showed the -12v ps that shows -22v is ok. I am not sure if that said it before but it makes me think its a ups or main pdu issue. On that matter I know something is plugged up and running on the ATS as there is 1 server it shows 0 total power output. I then plugged up my laptop which is basically a 200 watt PS 2 monitors and a test server up to it and it still showed as 0 Watt output. All my devices are powered on and each of the outlets are showing correct voltage when I use a multi-meter.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Hmm, OK.

Well the logs don't tell me anything new unfortunately. I still think either they need to be reset or likely replaced to resolve this each of these issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Well, I learned my lesson then, lol. Does your UPS have logs where it was reporting high frequency on the output? I wonder if your UPS has a frequency slew rate setting to tighten but I can't imagine if it did, that it should still somehow be outputting 120Hz. I have never seen that before but now I have!

I did check with engineering on the -12V power supply reading -22V. It should not have an affect on the ability on the frequency measurement. But, that one is also reading low input voltage..

We are interested in swapping that unit though for evaluation..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

well the thing is that the one with voltage issue is still alarming and it never had the frequency issue. The one that had the frequency issue did not have a voltage issue and is  now fixed. Another weird thing is it was source A that threw the alarm. The ups that was worked on was for Source B. I dont know but it is now fixed. Someone said to me that I may have a bugged upgrade on the voltage one. He said I should try down grading to previous firmware then reinstalling the newest firmware. Because I believe all the measurement tools are bunked. I mean all the outlets are measuring correctly with the multimeter and was able to power several devices. And no these leibert ups units does not give us any logs. They might give leibert logs but not us. I recently discovered a schnieder electrics building while driving on i75. I wouldnt mind dropping off the voltage unit if it is totally bunked. I know that they are out of warranty most likely.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

I don't agree with downgrading on this. If anything, resetting the ATS controller under the control menu is the next step. A botched firmware upgrade would not have this symptom.

If anything too, the unit is somehow mis-calibrated and that cannot typically be fixed by the user - you'd only be able to reset the controller in an attempt to do that.

Can I ask what state you're located in? Your serial numbers did not look out of warranty but I did not verify 100%.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Cincinnati Ohio. If I reset the controller will that cut power to the devices on the ATS?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

0 Likes
0
1247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:01 AM . Last Modified: ‎2024-03-18 12:13 AM

Yes, it will according to What does the "Reset ATS Controller" command accomplish on a Next Gen Rack Automatic Transfer Switch... - for 330-340ms it will cut the output unfortunately. I imagine most equipment will have a problem with that.

In Ohio, we don't have any APC/IT Business Unit facilities so it must be one of the other Schneider Electric BU's facilities. I am in Rhode Island and our facility that does most of the design and evaluation stuff on returned ATS units is in St. Louis, MO.

The one serial number I see for I believe the unit with the frequency issue is mid-late 2012 manufacture date and these have a two year warranty.

I think when you get some time as to not put a risk to the load, we should try to reset the ATS controller and if that does not work, ideally we could replace it for you and take a look at it because I am pretty sure it will still be in warranty at least until the end of 2014. Now on that other one that magically fixed itself when the electrician worked on the other source's UPS, I am honestly clueless unless there is a mistake on what is connected to what and he really did touch the UPS that is feeding that input.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of