Hi 2 all,
We have a SUA3000XLI and we attached 3 X SUA48XLBP.
Now I have some questions:
How can we test the SUA48XLBP if they work ? I stopped the power and the SUA3000XLI remained with only 2 / 5 lines in just 10minutes.
How much does it take for 3 X SUA48XLBP to get loaded ? I let them connected for about 24h by now.
The power on the mail UPS has the total power of him + battery packs ? So if it it 2 / 5 lines is overall or only the UPS power ?
Thanks in advance,
Alin.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:56 AM . Last Modified: 2024-03-13 02:00 AM
You don't necessarily need to do a calibration. These external batteries have no way to communicate with the main unit so you simply need to tell the ups(methods # 1 and #2) that you have 4 batteries total. Calibrations shouldn't be done unless absolutely necessary as they only drain your batteries and charge them back up. Once you update the software to show 4 batteries, you can let us know your runtime and load percentage. We can then confirm if the runtime is accurate.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:56 AM . Last Modified: 2024-03-13 02:00 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:56 AM . Last Modified: 2024-03-13 02:00 AM
Ok, solved it.
If anyone has this problem, here is the solution:
1. Install PowerChute
2. Set 4 batteries
3. Leave it for charging 48h
4. Make the Battery Calibration ( from PowerChute )
5. Leave it for charging 24h
6. Make a Battery Test to test the attached battery status
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:56 AM . Last Modified: 2024-03-13 02:00 AM
You don't necessarily need to do a calibration. These external batteries have no way to communicate with the main unit so you simply need to tell the ups(methods # 1 and #2) that you have 4 batteries total. Calibrations shouldn't be done unless absolutely necessary as they only drain your batteries and charge them back up. Once you update the software to show 4 batteries, you can let us know your runtime and load percentage. We can then confirm if the runtime is accurate.