SUA3000XL flashing all lights

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA3000XL flashing all lights
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:02 AM

0 Likes
10
5141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:02 AM

SUA3000XL flashing all lights

Hi all,

I've got a 3000XL here, with fairly new batteries, which was working great until one day, out of the blue, I got a bunch of beeps & every single light on the front panel flashing. I've attempted the various reset options, to no avail.

Yesterday, I dug my old 1400XL out, which has a duff battery, and tried one of the 3000XL batteries in it, and I get almost the same reaction - all the lights on the right hand side of the panel flash. A multimeter across the battery terminals shows 26-27 volts. I don't have any way of load testing a 24v battery, so that's as far as I've got.

I can't find any description of what the problem is, but obviously now it looks like the batteries are suspect, the next step is to buy some replacements; but can anyone tell me what the fault is?

Thanks!

Ade.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
1
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

Yes it was flashing all the LEDs and the fan works for some time and stop on its own till i touch the power off button then the lights stops blinking 

More So, I got the components from one of my scrapped APC UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:02 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:02 AM

Hello, 

All LEDs flashing - > electronics failure (likely relay welded) 

Right side (battery charge LEDs)  flashing->UPS detects that it can provide less than the minimum desired runtime if it was to operate on battery (2 or 5 mins depending on settings), this might be caused by bad battery, or no runtime calibration performed after replacing old and bad batteries

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

Hi Wolf,

Thanks for the reply - the flashing battery lights, would that include the unbalanced load & bad battery light (the red ones) as well as all the charge indicators?

Many thanks,

Ade.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

No, if the problem is the weak battery, then only the battery charge leds would flash (the 5 leds in a straight standing row at rightmost side).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

Hm, I'm getting the two red LEDs flashing as well.

So, here's the full symptoms, from power up for the 1000XL (not a 1400, that's another one I've got somewhere, can't find it just now):

Switch on utility power. Unit starts buzzing quietly (I guess this is the charge circuit?) for about 25 seconds, brief pause, buzzing resumes; repeat.

As soon as I press the ON button, the unit clunks, the mains light starts flashing, and the battery shows a number of bars (it's been four every time until just now, now it's one).

About 10 seconds later, the unit clunks again, the mains light goes off, and ALL of the battery lights (all 5 charge lights, and the three indicator lights) all start flashing. It does this until press the OFF button, at which point the buzzing resumes as above.

I'm going to leave it plugged in & switched off (but with the mains switched on) tonight, just in case it needs to put a big charge into the battery. If it behaves differently tomorrow, I'll post here.

Cheers!
Ade.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

The unit most likely has some sort of electronics failure. Try to cold start it. Ie. Mains not plugged in(only batteries are connected), and hold the on button pressed util you hear a beep, then release the on button during the beeping. It should start running on batteries. 

The normal start procedure with mains plugged in should look like as follows: on button pressed, brief beeping sound heard, battery charge leds become lit, online led flashing for several seconds, online led turns off, yellow on battery led turns on and clicking sound heard (and inverter buzzing sound), several seconds later yellow on battery led turns off and clicking sound heard, green online led turns on. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

Looks like there's a problem with the circuit.

I had similar issue with my SU2200. But mine started when i tried to upgrade it to 3000 by increasing the number o MOSPHETs. Mine, the faults was that when i try to start it, it goes off during self test leaving all the leds flashing but it was charging the batteries very well to 100%.

I was able to solve it though. And this was what i did.

The capacitors (C17 & 99) were empty with no caps on them. I filled those spots with the appropriate caps. Then i replaced the CT1 with another which i got from an SU3000. And the system is up and running beautifully well with my external (200AH) batteries.

If your issue is same with mine i guess it same problem that your stuff is having considering the fact that they're same model but different VA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

OK, I'm guessing it's an electronics fault then, possibly on both units.

Wolf - 

The 1000XL behaves basically the same if I cold-start it There's a big click (relay), a brief squeak from the inverter (usual noise), then a second big click and all the battery side lights flash.

I haven't tried the 3000XL again yet, as I have to swap the connector on one of the batteries, which is a chore...

It could still be duff batteries, although the 2 packs from the 3000XL seem to hold good charge. I do have a car battery charger, I could probably try each individual battery in turn with that... except it needs about 4 hands to do the test...

Samuel -

That sounds like something I could try; was yours flashing ALL of the lights (mains side too), or just the battery side? Reckon I need to swap those battery terminals back over & give the big boy another try anyway. Can I ask where you found the component specs? I've not removed any covers yet, are they printed on the board?

Thanks all!

Cheers,

Ade.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
0
5134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

OK, so I found some extra hands πŸ˜„ and tested 6 of my 8 batteries (all of which are conjoined into 4 24v units).

The two packs in the 3000XL are great. They both show around 13v per side, and on a 15 second 125A load test, dropped to between 8-10 volts, and recovered nicely to 12.5-13v (per side). The "OK" range on the battery tester is about 6-10 volts.

One side of one of the other packs is dead as a dodo. The other side is good. The fourth pack is totally dead.

So... I've 2 good solid batteries by the looks of it, and 2 failed UPS units. Grumble 😞 I'll look into fixing the 3000XL per Samuel's post, I think the 1000XL may as well be tossed. It's pretty ancient anyway, and it's so heavy the scrap value alone should get me a fried breakfast πŸ˜„

Cheers!
Ade.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

0 Likes
1
5135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:00 AM . Last Modified: β€Ž2024-03-18 01:01 AM

Yes it was flashing all the LEDs and the fan works for some time and stop on its own till i touch the power off button then the lights stops blinking 

More So, I got the components from one of my scrapped APC UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

toddbailey
Crewman toddbailey
Crewman

Posted: β€Ž2024-07-21 10:16 AM

In response to Anonymous user
0 Likes
0
2394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-07-21 10:16 AM

Seems like the apc has design issues.  I had a 3000rmxlu3 that had same fault condition and didn't run. I sent it ba k and the replacement works but the load indicator leds don't work. I'm thinking maybe buying tripplite

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore